New wood boiler user online and I know I have a learning curve with the operation. I've been lighting small fires in the Econoburn 100. It's operation alone has been pretty good so far. But, it's interface with the existing oil boiler has left us waking up to a cold house in the morning.
For some reason, the manual reset high limit aquastat on the oil boiler keeps going off. I have a thermal switch strapped to the supply line of the wood boiler to cut power to the oil boiler. The aquastat seems to trip just before the thermal switch is satisfied, whenever the oil boiler is still providing heat. I manually reset and it must have tripped overnight (assuming the same temperature range just as the wood boiler cools down and the thermal switch restores power to the oil boiler).
I have the HL aquastat set to 230degF. Is it possible that it sees these temps during the time period described above?
For some reason, the manual reset high limit aquastat on the oil boiler keeps going off. I have a thermal switch strapped to the supply line of the wood boiler to cut power to the oil boiler. The aquastat seems to trip just before the thermal switch is satisfied, whenever the oil boiler is still providing heat. I manually reset and it must have tripped overnight (assuming the same temperature range just as the wood boiler cools down and the thermal switch restores power to the oil boiler).