Need help with Air leak around flush mount direct vent gas fireplace

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.

SueS

New Member
May 4, 2023
1
NY
We have a brand new flush mount Enviro direct vent gas fireplace installed. There is air draft around the fireplace into the house at sides and along bottom. Installer said he insulated around the box….need help
 
The installer may have insulated, but did he also Sheetrock & seal all seams in the space containing the unit? You can try leaving the pilot burning during the colder months - if you can. It will keep the metal box warm. Also, you can try to seal the valve cavity with aluminum tape. There are openings in that area for gas & electrical wiring that allow for cold air to penetrate.