Hearth fans may remember that we moved to Cape Cod in June, to a house with five hot water heat zones and a gas hot water heater. The hot water heater, recently installed, was too tall for the flue setup and was backdrafting.
So I had a local heating/plumbing firm replace it with an 80 gallon SuperStor indirect, fired off the boiler. (It has a second set of coils for solar heating, and I'm planning on adding a couple of solar collectors next spring).
This firm added a sixth heating zone to the boiler and installed a TACO control box to provide DHW priority -- when the SuperStor calls for heating, the hydronic zones shut off.
The issue is that the TACO box also shuts off power to my Nest thermostats and they don't like it. They pop up with error messages (no power on power line) and the batteries start to discharge. When the DHW priority is satisfied, power goes back on to the Nests and they usually clear the error.
Here's a link to the factory TACO box wiring diagram: (broken link removed to http://www.taco-hvac.com/uploads/FileLibrary/102-092.pdf)
At our old house, we had a fifty year old boiler with three zones and indirect DHW. Similar setup with DHW priority, unknown electronics. Never had this issue with the Nests. In that house, and this, the Nests are each connected by two wires. One way to address the issue is to run a separate power line to feed each Nest, but I've checked, and I've only got two wires to each thermostat. Running an additional line for power would be a huge PITA.
The right approach would be to use a control box that retains power to the thermostats even if DHW priority is being called. I don't know if the TACO box can handle this or if I need a different box.
The service provider has not been particularly helpful, and I'm a little frustrated. I'd like to go to them with a definitive solution to the issue...
Would appreciate your recommendations on how to move forward...
Thanks!
So I had a local heating/plumbing firm replace it with an 80 gallon SuperStor indirect, fired off the boiler. (It has a second set of coils for solar heating, and I'm planning on adding a couple of solar collectors next spring).
This firm added a sixth heating zone to the boiler and installed a TACO control box to provide DHW priority -- when the SuperStor calls for heating, the hydronic zones shut off.
The issue is that the TACO box also shuts off power to my Nest thermostats and they don't like it. They pop up with error messages (no power on power line) and the batteries start to discharge. When the DHW priority is satisfied, power goes back on to the Nests and they usually clear the error.
Here's a link to the factory TACO box wiring diagram: (broken link removed to http://www.taco-hvac.com/uploads/FileLibrary/102-092.pdf)
At our old house, we had a fifty year old boiler with three zones and indirect DHW. Similar setup with DHW priority, unknown electronics. Never had this issue with the Nests. In that house, and this, the Nests are each connected by two wires. One way to address the issue is to run a separate power line to feed each Nest, but I've checked, and I've only got two wires to each thermostat. Running an additional line for power would be a huge PITA.
The right approach would be to use a control box that retains power to the thermostats even if DHW priority is being called. I don't know if the TACO box can handle this or if I need a different box.
The service provider has not been particularly helpful, and I'm a little frustrated. I'd like to go to them with a definitive solution to the issue...
Would appreciate your recommendations on how to move forward...