It seems the new NFPA requirement for 18" of floor protection in front of wood stove loading doors might actually have zero impact on most installations. Any manufacturer who submits a given stove for testing can get tested for a shorter hearth, and, if the stove passes, list that shorter hearth requirement in the installation manual. At that point, the tested listing would supercede the NFPA's standard requirement.
Example: NFPA 211 calls for 36" stove clearance to a combustible backwall, reduceable with proper wall shielding. A manufacturer can include rear shielding on a given stove model, submit it for testing, and achieve a listing much closer than this (we carry wood stove models that can be installed as close as 4" to an unshielded combustible backwall). In cases where a stove is listed for closer clearances than the standard clearance specified by NFPA 211, the listing takes precedence.
Example 2, more to the point: NFPA has required 16" clearance in front of a wood stove loading door for many years, and that's the standard most manufacturers test to. Most, but not all: Pacific Energy tested their Pacific D1 wood insert with a 2" raised hearth that extended just 10-5/8" in front of the loading door (a total of 16" measured from the fireplace facia). The D1 passed the test, and achieved a listing for installation with the shorter hearth. Even in Canada, which has long had an 18" standard hearth extension requirement.
Example 3, bringing it current: Hearthstone's new Equinox wood stove is still in the lab, undergoing clearance testing. The floor protection test has been completed, however, and the Equinox got a 16" hearth extension listing. This ocurred after the NFPA's switch to the 18" standard hearth requirement.
I've checked with the code inspectors in all five code jurisdictions our installers work in, and all are in agreement: they will continue to measure the hearth according to the manufacturer's listing as it appears in the installation manual.
The bottom line, as I see it: if you're installing a homemade wood stove, it had better be at least 36" from an unshielded backwall, and have floor protection extending at least 18" in front of the loading door. If you're installing a UL listed wood stove, the clearances and floor protection requirements listed in the installation manual will pass inspection.
Example: NFPA 211 calls for 36" stove clearance to a combustible backwall, reduceable with proper wall shielding. A manufacturer can include rear shielding on a given stove model, submit it for testing, and achieve a listing much closer than this (we carry wood stove models that can be installed as close as 4" to an unshielded combustible backwall). In cases where a stove is listed for closer clearances than the standard clearance specified by NFPA 211, the listing takes precedence.
Example 2, more to the point: NFPA has required 16" clearance in front of a wood stove loading door for many years, and that's the standard most manufacturers test to. Most, but not all: Pacific Energy tested their Pacific D1 wood insert with a 2" raised hearth that extended just 10-5/8" in front of the loading door (a total of 16" measured from the fireplace facia). The D1 passed the test, and achieved a listing for installation with the shorter hearth. Even in Canada, which has long had an 18" standard hearth extension requirement.
Example 3, bringing it current: Hearthstone's new Equinox wood stove is still in the lab, undergoing clearance testing. The floor protection test has been completed, however, and the Equinox got a 16" hearth extension listing. This ocurred after the NFPA's switch to the 18" standard hearth requirement.
I've checked with the code inspectors in all five code jurisdictions our installers work in, and all are in agreement: they will continue to measure the hearth according to the manufacturer's listing as it appears in the installation manual.
The bottom line, as I see it: if you're installing a homemade wood stove, it had better be at least 36" from an unshielded backwall, and have floor protection extending at least 18" in front of the loading door. If you're installing a UL listed wood stove, the clearances and floor protection requirements listed in the installation manual will pass inspection.