I’m planning on installing the Jotul F500 V3 in an alcove. The installation manual is fairly clear on the clearances and dimensions however I'm a little confused on exactly what material to use for the protection to make it a "protective alcove" per the manual and NFPA 211. So a few specific questions, number 2 being the most important question for me to get some insight:
1. The floor protection has to have an R value of 1.6. I have determined 1/2 durock R value is .39 from their website documentation. Micore 300 is 1.08. So if I use 1" of durock and 1/2 micore that would suffice for an R value of about 1.8 for the floor protection as long as my dimensions are correct. Does that sound about right? Does the floor have to have a 1" air gap off of the wood framing underneath or just the walls/ceiling because I haven't read anything about that?
2. The manual states to make a protective alcove "the walls and ceiling must be protected per NFPA 211. The wall protection must be elevated from the floor and from the combustable material 1". I understand the 1" air gap all the way around the walls and ceiling however what material will suffice for "wall protection"? So as I go in and read NFPA 211 Section 13, I see where they begin to say what protection is required to reduce clearances and in table 13.6.2.1 it lists several options, specifically in letter (f) it states 1" air gap with 1/2 thick non-combustable insulation board with the air space. And further down in section 13.6.2.7 it gives sort of a definition of what type of insulation board is required stating insulation material used as part of the clearance reduction system must have a thermal conductivity of less than 1.0 BTU-in/hr-ft squared- Fahrenheit. But what does all of that mean? What non-combustable insulation board do they mean?
What I'm gathering is so as long as the material on the wall/ceiling has a K factor of less than 1.0 and has the 1" air gap I am good? My plan was 1/2 micore (K factor of .48) of with 1/2 durock over top and then finish with 1/2 thin brick.
I just wanted to make sure I am interpreting the Jotul manual correctly and mainly the NFPA 211 Section 13 correctly when it defines what material to use for protection. Attached is a screenshot from the part of the NFPA 211 I was referring to. Thanks!
1. The floor protection has to have an R value of 1.6. I have determined 1/2 durock R value is .39 from their website documentation. Micore 300 is 1.08. So if I use 1" of durock and 1/2 micore that would suffice for an R value of about 1.8 for the floor protection as long as my dimensions are correct. Does that sound about right? Does the floor have to have a 1" air gap off of the wood framing underneath or just the walls/ceiling because I haven't read anything about that?
2. The manual states to make a protective alcove "the walls and ceiling must be protected per NFPA 211. The wall protection must be elevated from the floor and from the combustable material 1". I understand the 1" air gap all the way around the walls and ceiling however what material will suffice for "wall protection"? So as I go in and read NFPA 211 Section 13, I see where they begin to say what protection is required to reduce clearances and in table 13.6.2.1 it lists several options, specifically in letter (f) it states 1" air gap with 1/2 thick non-combustable insulation board with the air space. And further down in section 13.6.2.7 it gives sort of a definition of what type of insulation board is required stating insulation material used as part of the clearance reduction system must have a thermal conductivity of less than 1.0 BTU-in/hr-ft squared- Fahrenheit. But what does all of that mean? What non-combustable insulation board do they mean?
What I'm gathering is so as long as the material on the wall/ceiling has a K factor of less than 1.0 and has the 1" air gap I am good? My plan was 1/2 micore (K factor of .48) of with 1/2 durock over top and then finish with 1/2 thin brick.
I just wanted to make sure I am interpreting the Jotul manual correctly and mainly the NFPA 211 Section 13 correctly when it defines what material to use for protection. Attached is a screenshot from the part of the NFPA 211 I was referring to. Thanks!