Hi Dan, thanks for your input.
The goal is very basic; to control a zone circulator with outdoor reset. The supply temp will be from storage at 140-190 degrees. Ideally it would be variable speed ecm cruising on slow and steady, yes? My thought is that water temp sensor, outdoor temp sensor, thermostat calls demand and a control are what is necessary. Keep in mind I am not a plumber or hvac professional and will do anything myself rather than pay someone else. Not that I am just a cheapskate, but it is good to know what is going on with our technical and mechanical devices. Hence a DIY'er and eternal student.
The 256 and 356 differ in that the 356 has variable speed?
Does the "fixed" "varying" temperature of storage hinder ODR? Or, asked another way. Does the inability to control supply temp as in boiler control hinder ODR? ODR controls generally interact with boiler and circulation, yes?
OK, the 256 doing on/off will not work for your application. The 356 doing variable speed control of a single Taco conventional (permanent split capacitor type) circ is one of the choices I would look at for your application. If you're wondering what else I would look at, I bought my Tekmar injection pump controls new on EBay, so I would look for a deal, but most likely, something Tekmar. Depending on what else is going on, there are injection pump controls with more features, but the 356 would be a standard application as described.
As far as I know, I am not aware of an ECM type circ that does outdoor reset or works together with an OAT reset control. The ECM type cicr is far better at variable speed compared to conventional, it is made for variable speed, it just seems the market is not mature yet for ECM's. They do not offer all the different features now, wihch they will in the future. This question would have to go to the manufacturer's product representative, what is available today in an ECM circ with either internal or external OAT reset control.
The reset control will not care at all about the tank supply temp, including variances. It will simply calculate (reset) target setpoint supply HW after the circ, where the thermistor is, and ramp pump up or down to maintain the target temp. When supply is hotter at the tank, it will requires less speed to achieve setpoint, and more speed when tank temp is lower. It will not care otherwise.
If you had more than one circ to reset, because of the cost of the control, I would look at resetting a secondary header and take the regular speed zone circs or valves from that header.
And, imo, I would prefer the control and circ be separate for easier servicing. Easier to change a standard circ than a specialty circ with the control built in.
The zone thermostat trips the mix demand in the control. Have to look specifically at the manual to see if the control wants a voltage or closed contacts there. That starts the injection pump, but there are no smart features, like boiler protection, which you could use to stop the pump when the tank is cold.
If you want to disable the pump operation when the tank is cold, you may want to uprgade from the 356 to a reset control with boiler protection, and use the boiler protection thermistor to sense the tank temp.
I usually look at the whole, and in my own work, love puzzles, but hate assembling a puzzle when some of the pieces are missing. Still not enough information.