My old farmhouse is due for some upgrades or an overhaul to the heating system. I would appreciate some input to help me determine the best action plan. I'm located in south-central Pennsylvania in a 2500sq ft stone farmhouse with the plan of this being my forever home. I have 20 acres of forest plus my neighbor's forest that can supply me with endless firewood if I put in the effort.
The Current System: The main boiler is oil-fired with a DHW coil, 1 zone that supplies heat to my upstairs and downs stairs loops. Manual valves control the balance of the heat between the two hydronic baseboard loops. There is a fireplace insert boiler that is tied into the oil boiler with an aquastat and circulator. The two systems share the same water. The fireplace boiler is in my living room while the oil boiler is right below it in the basement. The fireplace boiler heats the oil boiler, sending heat to the baseboards and DHW coil. The equipment is believed to be circa 1984. Likely the oil boiler and fireplace insert boiler were new when an addition was added on to the house. Both are operational and in decent condition, if they are that old.
My first winter experience: The fireplace is working better than I expected. I gobbles up wood but I was able to maintain 70deg temps when it was single digits and windy this winter. Despite the mild winter, I believe that I burned 3 chords of wood during the month of January, so 15 chords+ for the year is what I'm planning for next year. I have boiled over the system a few times learning how it all works and was fortunate to not experience any significant power outages. The fireplace bubbles more than I would like. This is likely because air gets trapped at the high point and the water can begin to boil if you let the fire get too hot. There is no hot water storage in this system. Once the water temp reaches the high limit on the oil boiler (160F) it forces the circulator pump to distribute heat to the zone till a low limit (~140F) is reached. The oil boiler does not run until the low limit of 120f is reached during high demand or when the fire goes cold.
Operational Concerns:
I've briefly talked to Tarm and the local distributor for Froling to learn about indoor cordwood boilers. This type of system would work well in my basement because I have plenty of space and can easily get wood to it. The problem is the $20k pill to swallow for an all-new system. I'm not at a stage of life (early 30s) where this can absorb an investment like that. Maybe 10 years from now.
If I make no major change to the system components, I'm considering the following improvements to keep the budget-friendly and the system more reliable:
I'd love to hear all your input on this system. Thanks.
The Current System: The main boiler is oil-fired with a DHW coil, 1 zone that supplies heat to my upstairs and downs stairs loops. Manual valves control the balance of the heat between the two hydronic baseboard loops. There is a fireplace insert boiler that is tied into the oil boiler with an aquastat and circulator. The two systems share the same water. The fireplace boiler is in my living room while the oil boiler is right below it in the basement. The fireplace boiler heats the oil boiler, sending heat to the baseboards and DHW coil. The equipment is believed to be circa 1984. Likely the oil boiler and fireplace insert boiler were new when an addition was added on to the house. Both are operational and in decent condition, if they are that old.
My first winter experience: The fireplace is working better than I expected. I gobbles up wood but I was able to maintain 70deg temps when it was single digits and windy this winter. Despite the mild winter, I believe that I burned 3 chords of wood during the month of January, so 15 chords+ for the year is what I'm planning for next year. I have boiled over the system a few times learning how it all works and was fortunate to not experience any significant power outages. The fireplace bubbles more than I would like. This is likely because air gets trapped at the high point and the water can begin to boil if you let the fire get too hot. There is no hot water storage in this system. Once the water temp reaches the high limit on the oil boiler (160F) it forces the circulator pump to distribute heat to the zone till a low limit (~140F) is reached. The oil boiler does not run until the low limit of 120f is reached during high demand or when the fire goes cold.
Operational Concerns:
- Loss of power will boil over the fireplace boiler.
- The oil and wood boiler share the same water.
- Loss of power keeps me from heating the house effectively.
- The fireplace overheats water on startup if too big of a fire is made until the aquastat turns on the circulator.
- The fireplace makes bubbling noise more than desired requiring purging.
- I haven't looked in the chimney yet and it likely doesn't have a liner.
- No storage to bank heat excess heat causing the house to overheat on warm days from continuous fire.
- Cresote build up on water tubes in the firebox and are basically impossible to practically clean.
- Fire bricks are due for replacement.
- Oil boiler is likely near end of life.
- Fireplace circulator pump has a manual variable speed switch
- Oil boiler short cycles (rarely) to maintain water temp during high demand when the zones are full of cold water
I've briefly talked to Tarm and the local distributor for Froling to learn about indoor cordwood boilers. This type of system would work well in my basement because I have plenty of space and can easily get wood to it. The problem is the $20k pill to swallow for an all-new system. I'm not at a stage of life (early 30s) where this can absorb an investment like that. Maybe 10 years from now.
If I make no major change to the system components, I'm considering the following improvements to keep the budget-friendly and the system more reliable:
- Move the aquastat closer to the firebox to monitor water temperature more accurately and allow for the circulator to be more responsive to changing temperatures
- Electrically back up oil and wood boiler to be able to properly heat the house during a power outage. Bonus points for automatic standby options that don't break the bank.
- Add control of circulator pump speed to stabilize water temps in the firebox to reduce creosote buildup and reduce electric consumption.
- Separating the boilers so hot water is not shared between the systems in case the wood boiler overheats and blows the TPR.
- Add a bleeder valve at the top of the wood boiler to manually remove air in addition to hy-vent.
- Add temperature monitor/gauges somehow.
- Inspect the chimney and evaluate if a liner is needed/required. Possibly add EGT gauge because science....
- Continue remodeling the house to improve insulation and install new windows to reduce heat loss.
I'd love to hear all your input on this system. Thanks.