I have recently purchased a dealer refurbished 2008 Harman P68. It was running in my shop till I could get the hearth constructed in the house. In the shop it was a direct vent through the wall with 24" straight pipe. Moves it to the house hooked it up and the stove seems to have to much draft. It has no flame height and the flames are blue and 1/2" above and wrapped around the pellets. Appearing to be pulled into the holes in the burn pot. The venting installed is duravent all the joints have.been foiled taped proir to install. Starting at the stove a harman to pipe adapter then a 6" and 12" horizontal pipe next is a t with clean out cap on bottom. A 12" vertical then a 90 into the wall and a 12" section then the termination piece outside. Total EVL measuring joint to joint and adding for the T and 90 is 13.4791'
I hooked up a manometer for some draft measurements.
Cold stove,test mode unhooked flue
High was -.69-.73. Low .56-.59
Connected venting
High -.62-.65. Low -.52-.55
These numbers are the Low voltage draft screw in full counter clockwise position
Same test with Low voltage screws in full clockwise position
Unhooked flue
High .71-.73. Low .64-.67
Connected venting
High .63-.66. Low .56-.59
Input voltage to unit is 120.3 volts 60hz
Voltage at combustion blower 120.0 volts regardless of Low voltage switch position.
Stove has been thoroughly cleaned with vacuum and compressed air. All doors and accesses have been cleaned out.
Door gasket was adjusted using dollar bill and slight tension
No staus lights on.
Controls have been set at both room and stove temp.
Stove temp high ,feed at 4 stove will stay burning but side of firebox Temps never get above 260 degrees top of stove with distribution blower on high won't exceed 155 degrees
I'm burning somerset premium pellets which I was burning before with no problems.
Dealer which has been helpful is 4 hrs away. Is scratching his head. No local support so I'm trying here. Sorry for the long post just trying to get all the info out there that I had found
Has red wired probe and impedance of probe is 1100 ish ohm at 70 degrees temp(not sure if that's good or bad
Room temp setting had no effect on anything.
I hooked up a manometer for some draft measurements.
Cold stove,test mode unhooked flue
High was -.69-.73. Low .56-.59
Connected venting
High -.62-.65. Low -.52-.55
These numbers are the Low voltage draft screw in full counter clockwise position
Same test with Low voltage screws in full clockwise position
Unhooked flue
High .71-.73. Low .64-.67
Connected venting
High .63-.66. Low .56-.59
Input voltage to unit is 120.3 volts 60hz
Voltage at combustion blower 120.0 volts regardless of Low voltage switch position.
Stove has been thoroughly cleaned with vacuum and compressed air. All doors and accesses have been cleaned out.
Door gasket was adjusted using dollar bill and slight tension
No staus lights on.
Controls have been set at both room and stove temp.
Stove temp high ,feed at 4 stove will stay burning but side of firebox Temps never get above 260 degrees top of stove with distribution blower on high won't exceed 155 degrees
I'm burning somerset premium pellets which I was burning before with no problems.
Dealer which has been helpful is 4 hrs away. Is scratching his head. No local support so I'm trying here. Sorry for the long post just trying to get all the info out there that I had found
Has red wired probe and impedance of probe is 1100 ish ohm at 70 degrees temp(not sure if that's good or bad
Room temp setting had no effect on anything.