Just got the degree days for December and updated my performance record.
2010 – 2011 Heat Performance
Shop: 1536 sq ft; 21,500 cu ft; R19 walls, R39 ceiling, R10 floor, R20 perimeter, R10 to 2.5 ft below grade
Calculated Heat Load (base 60): 40,000 BTUH at -30F outdoor, 60F indoor
	
	
	
		
Floor sensor: constant 61F (1F differential)
Outdoor/Indoor air temperature:
+ 20F / + 58F
– 10F / + 55F
– 24F / + 50F
	
		
			
		
		
	
				
			2010 – 2011 Heat Performance
Shop: 1536 sq ft; 21,500 cu ft; R19 walls, R39 ceiling, R10 floor, R20 perimeter, R10 to 2.5 ft below grade
Calculated Heat Load (base 60): 40,000 BTUH at -30F outdoor, 60F indoor
		Code:
	
	Degree Days Normal (base 60) / Degree Days Actual (base 60) / Wood 6050 btu/lb
2010 /    Degree Days Normal    Degree Days     Lbs Wood     Lbs/DDA    BTUH 
2011        1970-2010 .............. Actual (DDA) ... Burned ................ Load
November        1076 ................ 873 ............... 1288 ..... 0.68 ..... 10,823
December        1559 ................ 1470 .............. 1855 ..... 1.26 ..... 15,084
January         1747
February        1375
March           1143Outdoor/Indoor air temperature:
+ 20F / + 58F
– 10F / + 55F
– 24F / + 50F
 
	 
	 
 
		 
 
		 
 
		 
 
		 
 
		 
 
		 
 
		 
 
		