Please take a look at my diagram. A few notes:
The boiler will be fired about twice weekly. I will fire up the boiler, turn on the boiler pump, open the solenoid, and turn on the pump in the storage tank to pull cool water off the bottom and deposit hot water on the surface. At the end of the firing, I will shut down these pumps, shut down the boiler, and close the solenoid. a 12 by 5 by 40 HX should be enough to transfer the 175K btu this boiler is capable of putting out.
Thermostat calls will activate the pump that pulls water off of the top of the tank and deposits it at the bottom, as well as the appropriate circulator.
The tricky part here comes down to the mixing valves. When the boiler is off, there shouldn't be any problem with the setup. However, when the boiler is firing there will be about 20 gpm of water flowing across the HX. This is enough to put about 5 feet of water pressure at the hot port of the mixing valve.
Using a standard mixing valve, will hot water leak across the hot port to the mix port and give me unwanted flow through my radiant loops?
Hot water will certainly leak across my hot water heater. I considered installing a zone valve here, but I think the easiest solution is to use a popit valve- a one way valve with an adjustable spring that will allow flow, but only above a certain pressure. The water flow in the system will make about 5 feet of head pressure; as long as this valve takes more than 5 feet to open, there will be no unwanted flow through that loop.
Any thoughts? I am about to spend quite a few dollars on this setup, so I would like for it to work!! I am most concerned with how to do the mixing valves.
Thanks!
The boiler will be fired about twice weekly. I will fire up the boiler, turn on the boiler pump, open the solenoid, and turn on the pump in the storage tank to pull cool water off the bottom and deposit hot water on the surface. At the end of the firing, I will shut down these pumps, shut down the boiler, and close the solenoid. a 12 by 5 by 40 HX should be enough to transfer the 175K btu this boiler is capable of putting out.
Thermostat calls will activate the pump that pulls water off of the top of the tank and deposits it at the bottom, as well as the appropriate circulator.
The tricky part here comes down to the mixing valves. When the boiler is off, there shouldn't be any problem with the setup. However, when the boiler is firing there will be about 20 gpm of water flowing across the HX. This is enough to put about 5 feet of water pressure at the hot port of the mixing valve.
Using a standard mixing valve, will hot water leak across the hot port to the mix port and give me unwanted flow through my radiant loops?
Hot water will certainly leak across my hot water heater. I considered installing a zone valve here, but I think the easiest solution is to use a popit valve- a one way valve with an adjustable spring that will allow flow, but only above a certain pressure. The water flow in the system will make about 5 feet of head pressure; as long as this valve takes more than 5 feet to open, there will be no unwanted flow through that loop.
Any thoughts? I am about to spend quite a few dollars on this setup, so I would like for it to work!! I am most concerned with how to do the mixing valves.
Thanks!