Hi All,
First post here but a longtime lurker and learner - thank you all for your willingness to share your knowledge and expertise.
Last year I purchased and installed a Regency H35 and really enjoyed the ambiance, heat output and look of the stove. Spring came and I turned it off completely for the summer, supply gas and valve on the stove. When a cold snap came through in early fall I decided to turn it back on only to find the heat output was drastically less, I'd guess at 25% of normal. The flame size was noticeably smaller and on the lowest heat setting there wasn't enough gas to burn. Naturally I called the shop that sold me the unit and they sent someone out to see whats going on. The technician tested it, tore it apart to check for blockages and supply gas pressure. It all checked out so he said it was probably the valve/manifold preventing enough gas from feeding the flame. A month later the same company finally came out with a new valve (warranty) and installed it. Unfortunately it didn't change anything, technician left... and a few new problems came up.
1) Flame/BTU output is still at about 25% of normal operation after a previous season of proper operation. No new appliances have been added and the 1/2" supply line runs directly from the meter, on its own run about 50'.
2) Smelled gas and found the tech failed to tighten a supply line from the valve to the burner orifice.
3) Previously, the flame would turn on from the pilot immediately and now there's a delay of about 20 seconds after something clicks.
4) After about 10 minutes of the flame on, another click and all flames turn off including the pilot.
I don't know much about gas valves, thermopiles/couples and what it takes to have one of these systems work properly, but Im also wondering if the company that's been out twice knows much either - despite common sense as one the largest fireplace dealers in the Denver area. So any advice would be great. Here's what I've done so far.
1) pressure tested the main supply line at 15 psi for 24 hours with no leaks
2) tested the supply gas pressure, 7.8 wc or just over .25 psi
3) double checked all connections before and after the fireplace valve
Anything else I can check/do before I call a different company? Clearly the competency of the dealer is subpar and inconsistent, but maybe Regency's quality is subpar too... Let me know your thoughts.
Thanks in advance,
Paul
First post here but a longtime lurker and learner - thank you all for your willingness to share your knowledge and expertise.
Last year I purchased and installed a Regency H35 and really enjoyed the ambiance, heat output and look of the stove. Spring came and I turned it off completely for the summer, supply gas and valve on the stove. When a cold snap came through in early fall I decided to turn it back on only to find the heat output was drastically less, I'd guess at 25% of normal. The flame size was noticeably smaller and on the lowest heat setting there wasn't enough gas to burn. Naturally I called the shop that sold me the unit and they sent someone out to see whats going on. The technician tested it, tore it apart to check for blockages and supply gas pressure. It all checked out so he said it was probably the valve/manifold preventing enough gas from feeding the flame. A month later the same company finally came out with a new valve (warranty) and installed it. Unfortunately it didn't change anything, technician left... and a few new problems came up.
1) Flame/BTU output is still at about 25% of normal operation after a previous season of proper operation. No new appliances have been added and the 1/2" supply line runs directly from the meter, on its own run about 50'.
2) Smelled gas and found the tech failed to tighten a supply line from the valve to the burner orifice.
3) Previously, the flame would turn on from the pilot immediately and now there's a delay of about 20 seconds after something clicks.
4) After about 10 minutes of the flame on, another click and all flames turn off including the pilot.
I don't know much about gas valves, thermopiles/couples and what it takes to have one of these systems work properly, but Im also wondering if the company that's been out twice knows much either - despite common sense as one the largest fireplace dealers in the Denver area. So any advice would be great. Here's what I've done so far.
1) pressure tested the main supply line at 15 psi for 24 hours with no leaks
2) tested the supply gas pressure, 7.8 wc or just over .25 psi
3) double checked all connections before and after the fireplace valve
Anything else I can check/do before I call a different company? Clearly the competency of the dealer is subpar and inconsistent, but maybe Regency's quality is subpar too... Let me know your thoughts.
Thanks in advance,
Paul