pump size question

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.
  • Hope everyone has a wonderful and warm Thanksgiving!
  • Super Cedar firestarters 30% discount Use code Hearth2024 Click here
Status
Not open for further replies.

wtrass

Member
Oct 30, 2011
26
southern tier NY
Installing a Vigas 40 with 1000 gallons storage. Using 1 1/4 copper lines and the boiler and tank are within 5 feet of each other. This is only to move water from boiler to tank- nothing else. How do I figure the pump size? thanks
 
Did you buy from AHONA? He gave me all the schematics, pump selection, and plumbing diagrams.

I have a 60, with a 0011 Taco. You're not moving as many BTUs.. but I have 1.5inch copper to and from my tanks.

JP
 
I have a 40 kW boiler. My loading unit uses a Grundfos 15-58 3 speed. Also have 1-1/4 pipe, and tanks close to boiler. I use it on low speed with no issues.
 
Status
Not open for further replies.