Been running my Quadrafire 1200i for years with no problems. This year, on start up, the convection fan will run for 5 seconds, shutdown for 10 seconds, and repeat. After 20 minutes of this, the fan will run longer and shut down for less time. Finally after an hour or so of this, the fan will run and stay running for as long as I'm calling for heat.  Tried all settings for the fan, same results. 
I replaced the snap disk 1, but no change in the stove at all. I checked the wires leading to the snap disk 1, what I don't understand is when the fan is running, there is no power running through the snap disk. When fan goes out, there is power present. (kind of the opposite of what I would expect). I disconnect the wires and the fan does not run (if the power goes to a relay, wouldn't this allow my fan to run)?
What am I not getting?
	
		
			
		
		
	
				
			I replaced the snap disk 1, but no change in the stove at all. I checked the wires leading to the snap disk 1, what I don't understand is when the fan is running, there is no power running through the snap disk. When fan goes out, there is power present. (kind of the opposite of what I would expect). I disconnect the wires and the fan does not run (if the power goes to a relay, wouldn't this allow my fan to run)?
What am I not getting?
 
	 
	 
 
		 
 
		 
 
		 You're reading voltage across the snap disc, right?  So with the fan running, the snap disc is closed, so it is at zero resistance and there will be no voltage dropped across it.  With the snap disc open (fan off), the total voltage is seen across the open circuit.  At least, that's what it sound like to me as far as your confusion on 'power'.
  You're reading voltage across the snap disc, right?  So with the fan running, the snap disc is closed, so it is at zero resistance and there will be no voltage dropped across it.  With the snap disc open (fan off), the total voltage is seen across the open circuit.  At least, that's what it sound like to me as far as your confusion on 'power'. 
 
		 
 
		 
 
		