My Vermont Castings Encore is being delivered today, and I am a little confused about the minimum clearance required for what I had planned to do. The manual of the stove lists the minimum clearances to combustibles with and without wall shields. However, all the wall shields are listed as having a 1" air space behind it. I was hoping I could use 3/4 Micore 300 (R-value=1.545) with 1.5" stone on top of that without using the airspace. However, I am not sure if that will meet code. I also checked NFPA 211 and table 13.6.2.1 has a clearance reduction chart. However, it just lists some examples without showing how it was calculated and what the R value is. (b) in the table lists 1/2 insulation board with 1" glass fiber without airspace, but doesn't list the R-value of it so I cannot really compare it. Section 13.6.2.7 says I can use insulation material that has a thermal conductivity of 1.0Btu-in/hr-ft2-F or less. This value is the inverse of an R value, so that should give me a value of 1/1.545=0.647. However, it doesn't say how much I can reduce it by. I haven't found any other references to clearances to combustibles without using airspace. Since my living room is kind of small, I'd like to keep it as close as possible to the wall while still meeting code (obviously). Can someone help me out with what I need or point me in the right direction with respect to minimum clearance without air space?
Thanks