That won't fly 1000 miles north.
. I do plan on adding a bang bang thermostat that's only real function will be to shut off the pump/ivalve at times when I have enough solar gain that the TRV's stop all flow. Overshooting for me is only due to solar gain or lots of occupants, never the radiant floors-the TRV's make sure of this.so your saying that if I bring the outdoor design temp down that it will bring the supply temps down? I will take pics of my system later to show you what I have.
So im gonna assume going from a design temp of 0 to -15 should help. Its a tekmar 356 outdoor reset. it mixes the water temp going into the radiant manifold. I wish there was a calculator or something on there website to see what my curve would look like. I will take pictures when I get home to give you guys an idea of my set up
I see the Tekmar next to the Taco zone control. The injection pump is to the left of the Webstone primary/secondary purge tee and out of sight. It looks like a nice setup.All of your zones are running off of one mixing temperature. If they don't all have the same heat loss or floor coverings then expect some heating variation in the zones. It looks like you have another remote manifold. i can see why you don't want to swap out thermostats as you must have a bunch!
im going to assume that lowering the room temp on the tekmar will have a greater effect
ideally how do you think my system should run?
Without changing the thermostats to a PWM capable version I would try and adjust the Characterized heating curve of the Tekmar to exactly match my building. This will lower the water temperature entering your floors to the point where they are just warm enough to heat the house at the desired indoor temperature. This will cause the radiant circulation pump(s) to run most of the time. Your thermostats would always be just below the setpoint and would keep the zone valves open and calling for a mix demand. This way you would not have heat swings assuming passive solar doesn't interfere and it also assumes that your outdoor sensor is in a shaded location outside away from any heat sources.
Usually it's impossible to achieve this perfectly without careful engineering but you can try. If you can't get it close enough with this technique then replacing with PWM thermostats (or maybe just in the hot rooms) will make it work.
I've described it already in the preceding posts but to summarize:
1)Lower the design temperature in the Tekmar mixing control to -18F or so (this should be set to your normally experienced low temperature).
2)Adjust the mix design temperature in the Tekmar to the desired radiant water temperature at this outdoor design temperature. Without knowing your current values it would be hard to guess but since your running hot now I would leave it at the current setting since the previous adjustment (1) will lower your floor temperatures.
3)Set the Room Temperature in the Tekmar to either 68-70 or what you set your thermostats for on average for comfort.
Run it for at least 24 hours and see what happens. If it's too warm adjust step 2 above lower, if it's too cold make it warmer. Make sure you give it sufficient time to adjust. It can take a day or two to stabilize.
Adjusting just the Room setting in the Tekmar as your contractor suggested I consider a hack, but it may work. The fact that the outdoor design temperature is no where close to what is experienced tells me the system isn't set up correctly.
I really think i'll try the wirsbo thermostat in my biggest room (living, kitchen) it is always off by a couple degrees in the day. another question is what sitting doing you think my variable speed pump should be on?
Gonna have three wirsbos in the mail today. All I have to do is hook up the two wires correct ? No other changes?