Finally got it done, so now all heating of the house and DHW is automated to heat from wood when the wood boiler is running or heat from Oil when its not.  Also have lower temps for the heat zones for the oil to kick in than when the wood boiler is running.
Also the DHW can only call for heat from the Oil boiler during the wee hours of the mornign which gives us a chance to build a fire in the evening and heat the water with wood boiler, if we dont then the oil will kick in and heat it.
Heres the control panel, outside view, the relays have LEDs in them so I can see whats on.
		![[Hearth.com] Relay Control Panel for heat system complete finally! [Hearth.com] Relay Control Panel for heat system complete finally!](https://www.hearth.com/talk/attachments/cimg2385-webp.180517/)
Inside view 120v blocks are insulated from the backboard. each 24vac fed item is individually fused so a failure of one item cannot kill the power supply for the entire sytem.
		![[Hearth.com] Relay Control Panel for heat system complete finally! [Hearth.com] Relay Control Panel for heat system complete finally!](https://www.hearth.com/talk/attachments/cimg2384-webp.180518/)
There are a couple of timers, the delay timer prevents the oil boiler from kicking on in between the wood boiler circulator kicking off while the wood boiler re-heats, IE if the house was really cold but was heating from wood I didnt want the oil boiler to kick on in between the wood boiler circulating cycles.
The other timer only allows the DHW to kick on the oil boiler from 11pm to 1am.
Heres a line diagram of the connections.
		![[Hearth.com] Relay Control Panel for heat system complete finally! [Hearth.com] Relay Control Panel for heat system complete finally!](https://www.hearth.com/talk/attachments/controllinediagram-webp.180519/)
This is the physical relay layout and individual connections to the relays, im not used to this relay setup so I created a view of this to help me wire it.
		![[Hearth.com] Relay Control Panel for heat system complete finally! [Hearth.com] Relay Control Panel for heat system complete finally!](https://www.hearth.com/talk/attachments/controlpanelrelaylayout-webp.180520/)
Last here is a diagram showing all the input and output connections. Probably overkill but I like things documented so I can look back at them for trouble shooting.
		![[Hearth.com] Relay Control Panel for heat system complete finally! [Hearth.com] Relay Control Panel for heat system complete finally!](https://www.hearth.com/talk/attachments/inputterminalconnections-webp.180521/)
Im planning on adding a second DHW boilermate in series so when we do a firing in the summer it will last two days. One does us one day so hopefully a second will go for two. Ill wire it so the aquastat on the one outputting to the house to the oil boiler, IE it will only heat one tank on the Oil boiler. THe second one that feeds the output one will have its aquastat wired up to heat when the wood boiler is running.
~ Phil
~ Phil
		![[Hearth.com] Relay Control Panel for heat system complete finally!](/talk/data/attachments/17/17375-296d21dca7bdaf1ef87b42c0a6ac5986.jpg?hash=lgtXejMWfc)