Hello
Working on an Englander 25-PDVC, the 25-PDV works the same.
Symptom:
The stove shuts down after about an hour.
Auger stops and then fire dies out.
Solution:
Since the bladder in the vacuum switch is weak and can let go after the stove heats up, I am replacing the both switches with a metal vacuum switch from Grainger.
On the Enviro I just pulled out the old vacuum switch, and set this new metal switch to the lowest WC about 17 and plug the hose onto the Top (low) negative pressure port and connected the wires to the common and NO - Normally open terminals and bingo - all set
The Englander stoves are unique,So I am trying to get this hookup straight. LOL
Is this correct?
OEM Englander Vac sw1
Door vacuum switch on the left side looking in from the back of the stove.
Wire Clips to:
Terminal 1 = Common and Terminal 2 = NO - Normally Open
Hose plugs on to:
Bottom P2 or Negative Pressure Port
This is what confused me. LOL
On Englander vacuum switches, the P1 Top Port is the Positive pressure port
OEM Englander Vac sw2
Exhaust vacuum switch on the right side looking in from the back of the stove.
Wire Clips to:
Terminal 1 = Common and Terminal 2 = NO - Normally Open
Hose plugs on to:
Bottom P2 or the Negative Pressure Port
-----------------------------------------------------------------------------------------------------------------
Replacement Cleveland Controls Metal Vacuum Switch. RFS-4150
Wire Clips to terminals 1 & 2 reading #s from Left to Right:
Terminal 1 = Common and Terminal 2 = NO - Normally Open
Hose plugs on to:
Top P1 (Marked Low) Negative pressure port
Stove fixing issue:
My dilemma is that I replaced the exhaust vac switch with the new one.
Same problem
Then put back the orig vac switch and
Replace the door vac switch with the new one. Same problem but stove died in 15 mins instead of an hour.
I put the door switch on the meter and if I tilted the switch it would change state. Certainly seems like a bad door vacuum switch!
The exhaust switch tested good on the meter but still could be intermittent!
Could both vacuum switches be bad? Is that like having 2 flat tires at once?
Stove is a 2004 MFD
The heat sensor looks fine and I checked the connections to the control panel.
The convection blower seems strong and is not sluggish!
Well, I replaced both vacuum switches and stove shuts down after 30 mins not 15 mins now?
Is it the heat sensor or the control board or both?
Working on an Englander 25-PDVC, the 25-PDV works the same.
Symptom:
The stove shuts down after about an hour.
Auger stops and then fire dies out.
Solution:
Since the bladder in the vacuum switch is weak and can let go after the stove heats up, I am replacing the both switches with a metal vacuum switch from Grainger.
On the Enviro I just pulled out the old vacuum switch, and set this new metal switch to the lowest WC about 17 and plug the hose onto the Top (low) negative pressure port and connected the wires to the common and NO - Normally open terminals and bingo - all set
The Englander stoves are unique,So I am trying to get this hookup straight. LOL
Is this correct?
OEM Englander Vac sw1
Door vacuum switch on the left side looking in from the back of the stove.
Wire Clips to:
Terminal 1 = Common and Terminal 2 = NO - Normally Open
Hose plugs on to:
Bottom P2 or Negative Pressure Port
This is what confused me. LOL
On Englander vacuum switches, the P1 Top Port is the Positive pressure port
OEM Englander Vac sw2
Exhaust vacuum switch on the right side looking in from the back of the stove.
Wire Clips to:
Terminal 1 = Common and Terminal 2 = NO - Normally Open
Hose plugs on to:
Bottom P2 or the Negative Pressure Port
-----------------------------------------------------------------------------------------------------------------
Replacement Cleveland Controls Metal Vacuum Switch. RFS-4150
Wire Clips to terminals 1 & 2 reading #s from Left to Right:
Terminal 1 = Common and Terminal 2 = NO - Normally Open
Hose plugs on to:
Top P1 (Marked Low) Negative pressure port
Stove fixing issue:
My dilemma is that I replaced the exhaust vac switch with the new one.
Same problem
Then put back the orig vac switch and
Replace the door vac switch with the new one. Same problem but stove died in 15 mins instead of an hour.
I put the door switch on the meter and if I tilted the switch it would change state. Certainly seems like a bad door vacuum switch!
The exhaust switch tested good on the meter but still could be intermittent!
Could both vacuum switches be bad? Is that like having 2 flat tires at once?
Stove is a 2004 MFD
The heat sensor looks fine and I checked the connections to the control panel.
The convection blower seems strong and is not sluggish!
Well, I replaced both vacuum switches and stove shuts down after 30 mins not 15 mins now?
Is it the heat sensor or the control board or both?
Attachments
-
EngVacuumSwForExhaustSC.webp137.6 KB · Views: 7,365
-
EngVacuumSwForDoorSC.webp76.3 KB · Views: 4,265
-
upgradedmetalvacuumswitchra.webp8.5 KB · Views: 1,751
-
ClevelandControlsRFS-4150front.webp216.2 KB · Views: 1,701
-
ClevelandControlsRFS-4150back.webp210 KB · Views: 1,567
-
ClevelandControlsRFS-4150front.pdf322.3 KB · Views: 1,578
-
ClevelandControlsRFS-4150back.pdf307.3 KB · Views: 487