Selkirk SuperVent vs. Duravent Galvanized

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.
  • Hope everyone has a wonderful and warm Thanksgiving!
  • Super Cedar firestarters 30% discount Use code Hearth2024 Click here

Mt Ski Bum

Minister of Fire
Feb 23, 2011
535
Dillon, Mt
So I recently found out that the old chimney in my house is actually not certified for air-tight solid fuel appliances (like my Avalon Pendleton), & that combined with stovepipe-ceiling box connection issues (thread here: https://www.hearth.com/talk/threads/chimney-support-box-issues-help.174432/ ), I am considering biting the bullet & replacing the whole Class A chimney.

Since I don't have a ton of money to work with, I want to go with either Selkirk's Supervent sold at Lowes or Duravent from Home Depot.

My question is: which one is better? are there advantages/disadvantages to each one?

I am tempted to go with Duravent's galavanized chimney because it is around $10 cheaper per section than the Duravent stainless steel or the Supervent. It appears to meet all the same standards as the others, but I've heard people on here before that are hesitant to go with a galvanized chimney over stainless- is there a reason for that?

Here are the 3 chimney types I am considering:

(broken link removed) (Duravent galvanized)

(broken link removed)
(Duravent Duraplus stainless)

https://www.lowes.com/pd/SuperVent-...ed-Double-Wall-Stainless-Chimney-Pipe/3134409 (Supervent stainless)

Any input is appreciated. Thanks!
 
I’d steer away from the air cooled dura-vent pipe. There’s no reason to avoid Selkirk pipe, it’s just fine.
 
I’d steer away from the air cooled dura-vent pipe. There’s no reason to avoid Selkirk pipe, it’s just fine.
it says the Duravents have a ceramic blanket insulation layer as well as an air layer on the website?
 
it says the Duravents have a ceramic blanket insulation layer as well as an air layer on the website?
Correct. The pipe just feels and looks cheap. I always see tons of wasp and mud dobber nests down inside of the cooling wall. Solid pack pipe is always a better option in my opinion.
 
it says the Duravents have a ceramic blanket insulation layer as well as an air layer on the website?
It is insulated. But it has half the insulation of double wall so the internal temps run much lower