Old Spark, I thought you had come to the decision to install a 6" liner after reading your posts at
https://www.hearth.com/talk/threads/72593/. Seems maybe you've changed your mind, and I would respectfully suggest that you consider changing it back.
There are ideal wood stove venting systems. For example, PE dialed your firebox in to work best with a 6" round, insulated chimney running straight up (no elbows) at least 15 feet.
There are totally unsatisfactory wood stove venting systems. These will cause problems like hard-to-start fires, smoke back-puffing into the room, no secondary burn, too-hot or too-cold stove temps, fires that go out, fires that burn up too quickly, etc. etc. etc.
Then there are marginal venting systems. These function adequately, but not at the level needed for optimum performance. Your system, for example, is not optimum for your stove: it is oversize, barely tall enough, totally uninsulated for the top 6 feet, only marginally insulated below, and it incorporates two 90's. It should be no surprise that your stove functions, but not at optimum performance.
Installation of an insulated 6" round stainless liner (and elimination of the 90's if possible) would transform your venting system into a much closer approximation of the system your stove was designed for, and couldn't help but improve its performance.