Lets see metal air intake tube, outside air temp below zero at times, so what is your trick if you don't mind sharing?
If it happens infrequently, heat seeker's and moey's ideas about just having something under the OAK tube to catch occasional drips works. In your climate, it would likely be useful to insulate the OAK intake duct itself (double wall pipe might be useful as well, but others from very cold climates can likely better comment on that). I believe there may be some new thimbles designed to help solve this as well, by using the heat of the exhaust to heat the incoming air a bit. For example, there are intakes that are above the exhaust pipe, which should help to some degree. I am not in a climate that cold, so have not seen them personally here.
Here is a thread from about three months ago. I believe post #4 references a Selkirk venting kit that addresses this issue via double walling, allowing the intake air to be warmed by the exhaust.
https://www.hearth.com/talk/threads/new-stove-owner-old-question.113161/
Ideally, you want two "loops" created: One that takes dry outside air, passes it through the combustion portion of the stove, and then vents it outside. No preheated (i.e., paid for) air with adequate moisture (~ 40 - 60% relative humidity) is used, and thus it is not pumped outside. The other loop takes preheated (paid for) indoor air, passes it through the side of the heat exchanger opposite the combustion area (thereby warming it), and passing it back into the room at a higher temperature, and with the same amount of moisture that it had before it was heated.
And for those who think their house is tight and that the venting of inside air via their stove "helps", IF you had a house that was so tight it needed an ERV / HRV (remember, most are not), then yes, theoretically you might be doing less damage with a pellet stove forcing this exchange. But it would still be an inefficient way to accomplish this, as it would be somewhat uncontrolled. An ERV / HRV with appropriate sensors is still likely better.
And on a side note, if Webbie is reading this: Your affiliate marketing is working GREAT! The banner ad above my reply box just changed to the Selkirk vent ad right after I used another window to find the thread above!