Is the vesta a good reliable controller and monitor out there. I think it looks like it would be worth it for my gasifier, I like the history of data that it appears to collect. Any thought, are there a lot of others using it?
BD your place must be insulated very well for that FHG 20 to heat all that space. For your boiler to burn for 8 to 9 hrs it must be in idle mode for a whileI have a Vesta system as well. Mine has been installed for one year now with no problems. I selected this controller for its versatility and ease of programing and installation. As you know already you get a controller that can be viewed from inside your home or from a remote location (PC or mobile device) though the port forwarding feature in our Router.
My controller is used to control the Return Water temperature to my Froling 20 boiler. I have a few modes of operation which allows the boiler to fire a full output or in an extended burn mode so that the fire will last from 8 to 9 hours. The storage tanks are monitored and the various heating loops are enabled depending on storage availability.
The last step for me is to create a graphic rather than using the list of inputs and outputs
View attachment 169866
BD your place must be insulated very well for that FHG 20 to heat all that space. For your boiler to burn for 8 to 9 hrs it must be in idle mode for a while
In the coldest weather my house needs about 1,100,000 BTUs over a 24 hours period, the house has R30 spray foam walls and R60 Roof (air sealed with 2-3" spray foam then topped up with cellulose. I wanted to design the boiler system so that I had enough storage to handle the load in the overnight and morning and buffer the heat from the boiler as it operates for up to 20 hours straight in the cold weather. The Froling can modulate from 100% to 50% output but you do not want to fire at 50% when you have just filled the fire box. This is where the Vesta controller adds functionality to the system. When I want a long burn I fill the fire box as full as possible on a 2 to 3" bed of coals. Then I set a State Variable which I call EXTENED BURN to ON. My program runs the boiler at 80 to 100% output for 2.5 hours which during this time burns off all the gasses and moisture. After this time the boiler goes to idle which is about 50% output (50% of 70,000 BTH for about 35,000) burning the charred wood for the remainder of the burn which last up to a total of 9 hours.
I control the firing rate by raising the return water temperature to the boiler via the mixing valve which the Vesta controls. With the Froling Lamda control the boiler does a great job of controlling the primary and secondary air through the burn. I just needed to help out a bit at the beginning of the cycle by keeping the firing rate up a bit to ensure that the primary air was not at a minimum while the gasses burned off. When I first tried the long burn at lower outputs the boiler would smoke for a couple of hours as the Primary air would be at a lower position to control the leaving water temperature and the secondary air would be at 100% with the stack O2 at less than the 8% target.
My system is just one year old and I find that the chimney only accumulates a fine layer of dust and the boiler is very clean with this operation. My flue temperatures range from 350°F at the beginning of the burn and 285°F once the boiler idles back. This was better than I expected and I cannot say enough about this boilers performance. Just light the fire, fill it and let it burn.
Thats excellent, does the Vesta communicate withe controller on the froling? I was talking to the froling dealer in Ontario he said The FHG also talks MODBUS and can integrate with your automation system .
How does the Vesta control the mixing valve,is it a loading valve also?
The Vesta does not communicate with the Froling. I monitor the Supply Water Temp from the boiler with the Vesta to determine if the boiler is cold, heating up, hot and cooling down. From here I set the Return water temperature setpoint to the boiler. The mixing valve is my loading valve, this valve is a 3-way mixing valve which uses a 0-10v signal from the Vesta[/QU
Does the Vesta control the boiler circ and the 3 way valve. Or does the Froling controller look after the boiler circ.
Sorry for all the questions , I might be repiping my near boiler stuff in the summer and I'm kind of interested in your setup. Would you happen to have a schematic of your sytsem? Is your 3 way valve similar to the one below?
Ok I am very interested, the vesta I am pretty much sold on. Dumb question, the loading valve is how much load or cooler water going back to boiler?The Vesta does not communicate with the Froling. I monitor the Supply Water Temp from the boiler with the Vesta to determine if the boiler is cold, heating up, hot and cooling down. From here I set the Return water temperature setpoint to the boiler. The mixing valve is my loading valve, this valve is a 3-way mixing valve which uses a 0-10v signal from the Vesta
OK, we have to *not* hijack this thread. Really. Just not fair.Alas, is propane also less expensive than pellets? Just kidding, but not really. How big is storage for that P4?
Ok I am very interested, the vesta I am pretty much sold on. Dumb question, the loading valve is how much load or cooler water going back to boiler?