The autofill valve is set at 12 psi. The expansion tank connection is near the autofill connection. Should I set the expansion tank to 12 psi, or a little higher?
Not paranoid...I do the same thing if I leave for any extended period. My brother returned from vacation to find a washing machine supply hose had failed, which flooded his basement. I try to err on the side of caution...easier to turn on well pump than to repair the damage.From my initial fill yesterday, I could see the pressure gauge read 12 psi, which was nice rather than futzing around and worrying about the well pressure. Now to fix the leaks! There's 0 psi in there now!
We typically turn the water off when we leave the house (paranoid, yes), and don't worry about it. I wonder where the water would go, anyway, where you wouldn't notice it?
Not paranoid...I do the same thing if I leave for any extended period. My brother returned from vacation to find a washing machine supply hose had failed, which flooded his basement. I try to err on the side of caution...easier to turn on well pump than to repair the damage.
The autofill valve is set at 12 psi. The expansion tank connection is near the autofill connection. Should I set the expansion tank to 12 psi, or a little higher?
if your operation psi in boiler is running at 12 psi or a little higher the expantion tank is not taking on no water drop tank down to 8 psi then the tank will take on water.. anything below 12 psi on the boiler when hot the bladder in the tank will not move and whats the use of having it if your only running 12 psi in the boiler...
An auto fill valve is a safety item, IMO. If your boiler overtemps (say a circulator went out), then the pressure safety valve blows. Your fire is still strong, and without more water, you could melt down your stove.
While this might be possible, a well-designed system will not let this happen. The boiler itself should shut down at the high limit point, and an overheat zone or loop, gravity fed, should be in place to bleed off the excess boiler heat production.An auto fill valve is a safety item, IMO. If your boiler overtemps (say a circulator went out), then the pressure safety valve blows. Your fire is still strong, and without more water, you could melt down your stove.
Not sure why that would be?
The expansion tank precharge pressure should be set lower than the pressure of the autofill valve. The expansion tank is not part of the system until the system pressure exceeds the pressure in the expansion. The relationship is typically 80% of the fill valve setting is what the tank air pressure should be. A fill valve setting of 15 psi would result in a 12 psi expansion tank precharge pressure. As Maple1 mentioned always measure the expansion tank pressure with the tank isolated from the system and open to the atmosphere so that you don't measure the water pressure in your system.