The following is copied from a private conversation I have been having with a forum member. Might be useful for others. The question asked of me was whether or not I had a build thread. My answer, with some minor edits:
I do not have a build thread, but I have had numerous posts about my system. The basic Tarm Solo Plus 40 (140,000 btuh) and the enhancements:
1) Single speed draft fan with a manual damper to adjust airflow. Early on experienced excessively high stack temps, into the 900F range. Discovered that the draft had a damper, which I then used to limit air flow. Temps reduced to 500F range maximum. Still high. See (7) below.
2) Manual lever to adjust portion of airflow to primary and to secondary. I have used this at a "set it and forget" setting. My wood is pretty uniform in MC and size of splits.
3) Draft fan is turned on manually. Aquastat that turns off the draft fan and boiler idles until temp drops a few degrees, which I have set at 190F boiler hot water temp. Actual fan off occurs at about 195F, back on at 190F.
4) High limit aquastat that triggers the gravity dump zone at an adjustable boiler hot water temp (210F is my setting).
5) Internal adjustable control with a sensor in the smoke box to turn off the draft fan when the burn is over and boiler is "cool." I have this set at 100C.
6) As supplied, no control over any circulators, either at start-up temperature or shut-down temperature. The boiler circ needed to be turned on and off manually. I changed the wiring so that the boiler circ would turn off when the draft fan turned off on cool down.
6a) Termovar boiler return water protection valve with fixed setting at 140F.
7) Not supplied with any turbulators in the firetubes. I made up and added chain turbulators. Effect was to reduce stack temp by about 100F from pre-turbulator burn conditions.
8) Added: digital temp controller that turns on the boiler circ at adustable boiler hot water supply temp. I have this set at 140F.
9) Added: digital temp controller that turns off the draft fan at high stack temp and then back on when stack temp drops. I have this set at 250C. Stack temp drops rapidly when the draft fan is turned off. I added this as a safety feature to help prevent a run-away burn. Glad I did, because twice I inadvertently failed to shut the bypass damper after loading wood, and this controller prevented dangerously high stack temp.
10) Added: linear actuator to open a window 6" when the boiler draft fan is turned on and shuts the window when the boiler is cool and shuts down.
11) Added: digital panel meters showing boiler supply/return temp, stack temp, storage top/middle/bottom temp, system supply/return temp.
12) Added: digital temp sensors at numerous locations to log data; used these to analyze issues that arose and satisfy my curiosity as to how the boiler and system actually were performing. I rarely log data any more. Last winter (2016) I bought a Raspberry Pi computer and now use that to log data if and when desired. Previously I had to use my laptop computer. Learned some Python programming to run on the Pi to do this.
My boiler and 1000 gal storage is in my shop, very short distance 1-1/4" copper piping between the boiler and storage and between storage and system. The boiler operates solely to charge storage. System draws and returns to storage as needed to maintain shop temperature. System heat is pex in-floor set to maintain a constant floor temp of 61F. The boiler circ is a Grundfos 15-58 set normally at M. Separate circs via an hx supply hot water to the in-floor. The hx is used because the boiler/storage is water and the in-floor has an antifreeze mix. In-floor supply temp via a mixing valve is set at 100F.
Originally I had an issue many have had: boiler over-heating and repeated idling; not enough hot water available to meet demand. My initial piping was 3/4" steel, about 70 feet round trip, which was wholly inadequate to handle boiler output of 140,000 btuh with a Taco 007. I then re-did with 1" steel, which was better but still inadequate. That's when I really started to learn hydronics. Then I built a new shop, moved the boiler and storage tank, and over the last 7 years everything has operated near perfect. I have been on a long learning curve to understand hydronics, especially btus, gpm flow rate, pump head, circulators and heat exchangers.
Happy Holiday season to all, and don't shy away from keeping your feet in hot water.
I do not have a build thread, but I have had numerous posts about my system. The basic Tarm Solo Plus 40 (140,000 btuh) and the enhancements:
1) Single speed draft fan with a manual damper to adjust airflow. Early on experienced excessively high stack temps, into the 900F range. Discovered that the draft had a damper, which I then used to limit air flow. Temps reduced to 500F range maximum. Still high. See (7) below.
2) Manual lever to adjust portion of airflow to primary and to secondary. I have used this at a "set it and forget" setting. My wood is pretty uniform in MC and size of splits.
3) Draft fan is turned on manually. Aquastat that turns off the draft fan and boiler idles until temp drops a few degrees, which I have set at 190F boiler hot water temp. Actual fan off occurs at about 195F, back on at 190F.
4) High limit aquastat that triggers the gravity dump zone at an adjustable boiler hot water temp (210F is my setting).
5) Internal adjustable control with a sensor in the smoke box to turn off the draft fan when the burn is over and boiler is "cool." I have this set at 100C.
6) As supplied, no control over any circulators, either at start-up temperature or shut-down temperature. The boiler circ needed to be turned on and off manually. I changed the wiring so that the boiler circ would turn off when the draft fan turned off on cool down.
6a) Termovar boiler return water protection valve with fixed setting at 140F.
7) Not supplied with any turbulators in the firetubes. I made up and added chain turbulators. Effect was to reduce stack temp by about 100F from pre-turbulator burn conditions.
8) Added: digital temp controller that turns on the boiler circ at adustable boiler hot water supply temp. I have this set at 140F.
9) Added: digital temp controller that turns off the draft fan at high stack temp and then back on when stack temp drops. I have this set at 250C. Stack temp drops rapidly when the draft fan is turned off. I added this as a safety feature to help prevent a run-away burn. Glad I did, because twice I inadvertently failed to shut the bypass damper after loading wood, and this controller prevented dangerously high stack temp.
10) Added: linear actuator to open a window 6" when the boiler draft fan is turned on and shuts the window when the boiler is cool and shuts down.
11) Added: digital panel meters showing boiler supply/return temp, stack temp, storage top/middle/bottom temp, system supply/return temp.
12) Added: digital temp sensors at numerous locations to log data; used these to analyze issues that arose and satisfy my curiosity as to how the boiler and system actually were performing. I rarely log data any more. Last winter (2016) I bought a Raspberry Pi computer and now use that to log data if and when desired. Previously I had to use my laptop computer. Learned some Python programming to run on the Pi to do this.
My boiler and 1000 gal storage is in my shop, very short distance 1-1/4" copper piping between the boiler and storage and between storage and system. The boiler operates solely to charge storage. System draws and returns to storage as needed to maintain shop temperature. System heat is pex in-floor set to maintain a constant floor temp of 61F. The boiler circ is a Grundfos 15-58 set normally at M. Separate circs via an hx supply hot water to the in-floor. The hx is used because the boiler/storage is water and the in-floor has an antifreeze mix. In-floor supply temp via a mixing valve is set at 100F.
Originally I had an issue many have had: boiler over-heating and repeated idling; not enough hot water available to meet demand. My initial piping was 3/4" steel, about 70 feet round trip, which was wholly inadequate to handle boiler output of 140,000 btuh with a Taco 007. I then re-did with 1" steel, which was better but still inadequate. That's when I really started to learn hydronics. Then I built a new shop, moved the boiler and storage tank, and over the last 7 years everything has operated near perfect. I have been on a long learning curve to understand hydronics, especially btus, gpm flow rate, pump head, circulators and heat exchangers.
Happy Holiday season to all, and don't shy away from keeping your feet in hot water.