Hello all, this is our second winter heating our house and dhw with a conventional wood boiler and loving it. But this winter I have an intermittent problem that concerns me about leaving for an extended time. Several times I have gone to add wood and found it over temping and the over temp aqustat activated. But my dump zone is my first floor zone and looking into it each time I find the zone valve for that zone not open. Power is applied to it but its closed. If I remove power to it and re-apply the power it opens. The zone valves I used are Taco motorized EBV valves, normally closed. I selected them because they did not use a spring to close the valve but instead a charged capacitor that when power is removed it uses that power to run the motor to close it. Also when the valve is in the OPEN state the current draw is low, the valve is not spring loaded and does not take any current draw to keep the valve open...
I use standard relays to control the pumps and zone valves. each valve is fused separately from the 24vAC supply. This is my control setup.
https://www.hearth.com/talk/threads/38912/
But three times in the past month it has failed to open. Im afraid to leave for an extended time and have the house not be heated because of a stuck zone valve.
Any thoughts / suggestions?
Thanks
~ Phil