is concrete good for a hearth??

Post in 'The Hearth Room - Wood Stoves and Fireplaces' started by lime4x4, Jan 24, 2006.

Thread Status:
Not open for further replies.
  1. lime4x4

    lime4x4
    Expand Collapse
    Member

    Joined:
    Nov 18, 2005
    Messages:
    134
    Likes Received:
    0
    Loc:
    Northeast Pa
    Come spring i want to get rid of my silly looking black hearth mat and build a 4" thick concrete hearth with a slate design etched into the concrete before it sets up? Will this provide good fire protection?
    It will be underneath a harman magnum coal stoker?
     
    Collapse Signature Expand Signature

    Helpful Sponsor Ads!





  2. MountainStoveGuy

    MountainStoveGuy
    Expand Collapse
    Minister of Fire

    Joined:
    Jan 23, 2006
    Messages:
    3,654
    Likes Received:
    2
    Loc:
    Boulder County
    You need to research the r value required for the bottem of the appliance. Poured concrete has .08 r value/inch.
    Ryan
     
    Collapse Signature Expand Signature
  3. lime4x4

    lime4x4
    Expand Collapse
    Member

    Joined:
    Nov 18, 2005
    Messages:
    134
    Likes Received:
    0
    Loc:
    Northeast Pa
    the manual gives no spec just says the floor must be non-combustable.the actual fire is about 2 feet off the floor and there is a ash pan under that sits about 6 inches off the floor
     
    Collapse Signature Expand Signature
  4. MountainStoveGuy

    MountainStoveGuy
    Expand Collapse
    Minister of Fire

    Joined:
    Jan 23, 2006
    Messages:
    3,654
    Likes Received:
    2
    Loc:
    Boulder County
    Maybe this will help.
    Floor Protection for Unlisted Stoves (from NFPA 211)

    Size: Floor Protection shall extend to at least 18" from all sides of the appliance.

    Construction: The basic floor protection specified by NFPA applies to stoves with legs over 6" in height. This means that the floor of the stove combustion chamber should be at least this height above the floor surface. The standard calls for:
    1. Closely spaced 2" thick masonry units (brick or cinderblock/patio block.
    2. Top cover of 24 gauge sheet metal.

    For stoves with legs from 2" to 6" in height, the standard calls for:
    1. Hollow 4" blocks set on their side so that the ventilated spaces line up horizontally. The ends should remain open for proper flow of cooling air.
    2. Top cover of 24 gauge sheet metal.
     