Look what I found when I tore my old fireplace out.

tlhfirelion Posted By tlhfirelion, Jul 10, 2008 at 8:16 PM

Thread Status:
Not open for further replies.
  1. rdrcr56

    rdrcr56
    New Member 2.
    NULL
    

    Sep 8, 2006
    216
    0
    In the picture of your opening is that horizontal stud what you are talking about as 46 in. high?
     
  2. tlhfirelion

    tlhfirelion
    Feeling the Heat 2.
    NULL
    

    Aug 6, 2007
    300
    3

    excellent reply man, I understand what you are explaining and thats what I was seeing in my head. I guess weather the chase is there or not is irrelevant since it's got much more clearance than is needed so it's a non issue. The only problem I see with that is how to access the chase from the outside to clean out the "T" but thats an easier problem to solve from the outside and for another day. In the chase area I assume I can use the galvanized double wall correct?
     
  3. tlhfirelion

    tlhfirelion
    Feeling the Heat 2.
    NULL
    

    Aug 6, 2007
    300
    3
    No I'm referring to the beam that can only be seen from inside the chase that is towards the top of the wall.
     
  4. rdrcr56

    rdrcr56
    New Member 2.
    NULL
    

    Sep 8, 2006
    216
    0
    Well I guess I cant picture the framing of your wall, so what I'm trying to get across is that where the ceiling and the wall meet that is where the load bearing joist should be, you should be able to remove the wall that was above your old fireplace up to close to the ceiling.
     
  5. tlhfirelion

    tlhfirelion
    Feeling the Heat 2.
    NULL
    

    Aug 6, 2007
    300
    3
    You are correct, we are seeing the same thing in our head, just explaining it different. That load bearing joist is what is in the way of me getting my proper clearances for an alcove set up. No worries man thanks for your help.
     
  6. tlhfirelion

    tlhfirelion
    Feeling the Heat 2.
    NULL
    

    Aug 6, 2007
    300
    3
    I got delayed on working on my fireplace but am back at it now. I have constructed the hearth pad out of 2X4 construction (14" on center) with 1" plywood on top and facing the front of it. (it is a raised hearthpad) My plan is to now put 2 layers of durock on this plywood, the the thinset and the hearth stones/stone veneer. I will have have all the proper clearances per my stoves manual. Before I continue, would you agree or disagree that so far I am doing this correctly?
     
  7. tlhfirelion

    tlhfirelion
    Feeling the Heat 2.
    NULL
    

    Aug 6, 2007
    300
    3
    Actually it appears (see chart from hearth.com below) I could easily use only 1 sheet of durock on the hearth pad. My stove manual states I need floor protection equiv. to 3/8th" millboard and an r value of .446. I could use only 1 sheet of durock on my 1" plywood, and then put the stove veneer on that and still be over the requirements. Correct?
     
  8. begreen

    begreen
    Mooderator 2.
    NULL
    
    Staff Member

    Nov 18, 2005
    61,605
    7,877
    Loc:
    South Puget Sound, WA
    Considering that at some point in the future you might want to upgrade the stove, perhaps build it slightly oversized and over-spec? If you agree, put a layer of micore on top of the plywood, then a layer of sheetmetal, then a single top layer of durock. Screw the sandwich together per durock's recommended interval. That would give you a more future-proof hearth for just a few more bucks.
     
  9. tlhfirelion

    tlhfirelion
    Feeling the Heat 2.
    NULL
    

    Aug 6, 2007
    300
    3
    Well I can tell you we are talking about building a home in about 2 years so this will be our last hearth construction here. There is zero chance of us upgrading the stove in this home. I must admit I was rather surprised at how small of an r value this stove needed but I must remember it is a small stove compared to those that some of you guys have. As always thanks for your reply!
     
  10. fossil

    fossil
    Accidental Moderator 2.
    NULL
    
    Staff Member

    Sep 30, 2007
    10,537
    2,416
    Loc:
    Bend, OR
    This copied & pasted from USG:

    "DUROCK Brand Cement Board has an R value of 0.26"

    Rick
     
  11. tlhfirelion

    tlhfirelion
    Feeling the Heat 2.
    NULL
    

    Aug 6, 2007
    300
    3
    OK, so I have 1" plywood, 1 sheet of durock, then hearth stone and mortar and I only need .446 for my r value. Well I feel I am operating safely by proceeding. Thanks man.
     
  12. begreen

    begreen
    Mooderator 2.
    NULL
    
    Staff Member

    Nov 18, 2005
    61,605
    7,877
    Loc:
    South Puget Sound, WA
    Got it. In that case, proceed as planned.
     
  13. tlhfirelion

    tlhfirelion
    Feeling the Heat 2.
    NULL
    

    Aug 6, 2007
    300
    3
    Right on thank you.
     
  14. fossil

    fossil
    Accidental Moderator 2.
    NULL
    
    Staff Member

    Sep 30, 2007
    10,537
    2,416
    Loc:
    Bend, OR
    Not sure why you keep mentioning the 1" of plywood. Plywood's a combustible. All the required insulative value needs to be between the stove and the combustible. The plywood has nothing to do with the required r-value of the hearth. Just wanting to make sure I understand. The mortar buys you next to nothing, and I'm not sure what you mean by hearth stone, but if it's some sort of stone veneer, than it doesn't have much r-value either. Rick
     
  15. begreen

    begreen
    Mooderator 2.
    NULL
    
    Staff Member

    Nov 18, 2005
    61,605
    7,877
    Loc:
    South Puget Sound, WA
    Rick, thanks for waking me up - firelion, is this for the Century 27007 stove? I assumed you were following the manual which now that I re-read it calls for R.893 or better on the hearth. So far you have only R .52. If you go back to my original instructions you will be good to go.

    Are my docs in conflict with your's?

    EDIT:
    Argh! Documentation department please! Now I see what you are seeing too. And it says .446 for the same 3/8" millboard. So you are OK as you are following the stove specifications.
     

    Attached Files:

  16. tlhfirelion

    tlhfirelion
    Feeling the Heat 2.
    NULL
    

    Aug 6, 2007
    300
    3
    Yes they do conflict my docs. I am looking right at it and the portion os the 3/8th inch millboard and the floor protector must have a min. r value of .446. Would the legs versus pedestal have anything to do with this?
     
  17. tlhfirelion

    tlhfirelion
    Feeling the Heat 2.
    NULL
    

    Aug 6, 2007
    300
    3
    actually I think the leg/ped. thing is the difference. If you look on the image you put up, up in the top left hand corner you will see a pic of your stove and the clearance pic to the roof. Yours shows the stove with legs and mine with the stand.
     
  18. begreen

    begreen
    Mooderator 2.
    NULL
    
    Staff Member

    Nov 18, 2005
    61,605
    7,877
    Loc:
    South Puget Sound, WA
    No, see above post. This is a mess up with Century's documentation or you have a different model. What is the correct model number for your stove?

    You can go by the specs you have. If questioned, you have the paperwork to prove it.
     
  19. tlhfirelion

    tlhfirelion
    Feeling the Heat 2.
    NULL
    

    Aug 6, 2007
    300
    3
    what on earth?? So which manual do I follow?
     
  20. tlhfirelion

    tlhfirelion
    Feeling the Heat 2.
    NULL
    

    Aug 6, 2007
    300
    3
    Well, thats good but is this a major safety problem or what? How do I know my paperwork is correct and not yours or vice versa?
     
  21. begreen

    begreen
    Mooderator 2.
    NULL
    
    Staff Member

    Nov 18, 2005
    61,605
    7,877
    Loc:
    South Puget Sound, WA
    Follow your paperwork - what the exact model of your stove. The higher hearth R value is for the 27007.
     
  22. tlhfirelion

    tlhfirelion
    Feeling the Heat 2.
    NULL
    

    Aug 6, 2007
    300
    3
    I don't have a clue why I mentioned it, guess I just wanted to brag. lol
     
  23. tlhfirelion

    tlhfirelion
    Feeling the Heat 2.
    NULL
    

    Aug 6, 2007
    300
    3
    I have the fw240007 and it says that on the sticker on the back of my stove. The manual says for either 0007 or 0008.
     
  24. fossil

    fossil
    Accidental Moderator 2.
    NULL
    
    Staff Member

    Sep 30, 2007
    10,537
    2,416
    Loc:
    Bend, OR
    If you need .446, then slap in two layers of 1/2" Durock and be done with it. Forget about figuring in the mortar and stone veneer, they have r-values an order of magnitude below Durock...they'll add up to 0.0xx, just ignore them. Rick
     
  25. begreen

    begreen
    Mooderator 2.
    NULL
    
    Staff Member

    Nov 18, 2005
    61,605
    7,877
    Loc:
    South Puget Sound, WA
    That probably explains the difference. Earlier on I asked if this was the 270007 and got an affirmative. It seems the 270007 is a bigger stove and requires a bit more protection. Sorry for the confusion. It doesn't explain the confusing language of the docs, but you are covered. Just screw that sucker together and put your heater on it.
     