    I have come to the conclusion that using radiators with trv valves and a alpha pump to circulate is about as simple as a boiler setup can get. What are the drawbacks to this setup? I am trying to setup a super simple cheap heating system to get into the house I am restoring with out spending a ton of money on the system and the plumber.

    Helpful Sponsor Ads!





  2. Chris Hoskin

    Chris Hoskin TarmSalesGuy

    Joined:
    Aug 29, 2008
    Messages:
    453
    Loc:
    Lyme, NH
    I agree. Add a buffer tank and an outdoor reset mixing valve and you are good to go.
    woodsmaster likes this.
  3. woodsmaster

    woodsmaster Minister of Fire

    Joined:
    Jan 25, 2010
    Messages:
    2,511
    Loc:
    N.W. Ohio
    I second the outdoor reset.
  4. Floydian

    Floydian Feeling the Heat

    Joined:
    Dec 12, 2008
    Messages:
    436
    Loc:
    Southwestern VA
    Hi James,

    Are you installing a gassifier and storage?

    I almost went with panel rads with TRV's but in the end I went with low temp radiant floors. I HAD to have the TRV's though so I got the capillary tube variety.
    I have seven loops on my manifold, an alpha on constant circulation, each loop has a TRV and I use a Taco ivalve with outdoor reset. It's works beautifully.
    I planned for 120::F supply temp at my design temp so for avg outdoor temps I see maybe 100 to 110::F. It's really nice watching the supply temp rise as the outdoor temp falls and vice versa.

    More on my setup in the link in my signature.

    Have you run the room by room heat loss calculation?
    This is important for sizing the panel rads at a given supply temp, figuring flow rates and your reset ratio as well.

    Keep us updated.... with pictures preferably::-)

    Noah
  5. James Grizzard

    James Grizzard New Member

    Joined:
    Oct 30, 2013
    Messages:
    10
    Loc:
    Northern New Mexico
    Tryin to just get into the house, I don't even know if I will get a wood boiler till after I get in. For now its gonna be a cheap craigslist natty boiler and I will eventually add a wood boiler of some sort I have a guy close to me selling a EKO40 and a Empire Elite 100 for around the same price and I will hopefully grab one and find a old propane tank for storage.
  6. BoilerMan

    BoilerMan Minister of Fire

    Joined:
    Apr 16, 2012
    Messages:
    1,605
    Loc:
    Northern Maine
    If you like the radiator look, have you considered some reclaimed CIO rads, those would be cheaper that the Mysons. I have some upstairs I bought last year, sandblasted and painted them. Worst part is lugging them :confused:

    TS
  7. James Grizzard

    James Grizzard New Member

    Joined:
    Oct 30, 2013
    Messages:
    10
    Loc:
    Northern New Mexico
    If I would have known I was gonna be doing this I would have a bunch. My contractor/buddy restored a 3 story 1800's Wells Fargo building earlier this year that was full of them. They all went to scrap even though I told him to save them. I looked on craigslist and found none for sale and the problem with New Mexico is most houses are either dirt or new build so not many old style radiators. My buddy is totally against the wood boiler and I can't wait to show him that I can have d hot water year round, keep my house nice and warm(no cold mornings cause I cant afford natural gas or the wood stove goes out) and get a free hot tub with a burnt heating element and run the sucker with my boiler for the same money he uses keeps his hot tub hot.