nothing but problems with a hearthstone heritage

Post in 'The Hearth Room - Wood Stoves and Fireplaces' started by new burner, Oct 31, 2009.

Thread Status:
Not open for further replies.
  1. new burner

    new burner
    Expand Collapse
    New Member

    Joined:
    Oct 31, 2009
    Messages:
    50
    Likes Received:
    0
    Loc:
    northern illinois
    here is another picture from outside.
     

    Attached Files:

    Helpful Sponsor Ads!





  2. new burner

    new burner
    Expand Collapse
    New Member

    Joined:
    Oct 31, 2009
    Messages:
    50
    Likes Received:
    0
    Loc:
    northern illinois
    blacktop,
    you are right its not Hearthstones fault about the chimney. That was done by the dealer, and not very well. It is totally messed up.
    But fixing the draft will only mask the other problems with the stove. The draft does need to be delt with.
    The stove is messed up though. Whether or not the stove problems were caused from the dealer, manufacturer, or in shipping, I dont know.
    But no one wants to fess up.
     
  3. new burner

    new burner
    Expand Collapse
    New Member

    Joined:
    Oct 31, 2009
    Messages:
    50
    Likes Received:
    0
    Loc:
    northern illinois
    does anyone know if there is a serial number stamped on the stove, other than the tag in the back?
    I seen some numbers stamped on the inside, opposit of the side door.
     
  4. tutu_sue

    tutu_sue
    Expand Collapse
    New Member

    Joined:
    Jan 21, 2006
    Messages:
    489
    Likes Received:
    0
    Loc:
    Northern NJ
    I recall there being a certificate that was in an envelope with the owner's manual (a must read), may have had serial number on it. Not positive though. How tall is your venting system overall?
     
    Collapse Signature Expand Signature
  5. Fsappo

    Fsappo
    Expand Collapse
    Minister of Fire

    Joined:
    Apr 9, 2008
    Messages:
    4,331
    Likes Received:
    180
    Loc:
    Central NY
    Holy moly. I'm not one to condemn a fellow brick and mortar retailer but from stove to chimney cap you got hosed. Like someone else suggested in another thread, Video the stove in action and Youtube it. The dealer should be ashamed, the chimney redone with proper height and bracing, and attic insulation shield and god(sorry muslims) knows what else they missed. Also, I would demand a new stove NOW before the shop gets any busier. That is a disgrace to our industry
     
  6. gyrfalcon

    gyrfalcon
    Expand Collapse
    Minister of Fire

    Joined:
    Dec 25, 2007
    Messages:
    1,828
    Likes Received:
    197
    Loc:
    Champlain Valley, Vermont
    Very well said. Agree entirely.

    (PS Muslims actually believe in God. So do Jews, just in case that was also unclear.)
     
    Collapse Signature Expand Signature
  7. Fsappo

    Fsappo
    Expand Collapse
    Minister of Fire

    Joined:
    Apr 9, 2008
    Messages:
    4,331
    Likes Received:
    180
    Loc:
    Central NY
    I keep forgetting that
     
  8. new burner

    new burner
    Expand Collapse
    New Member

    Joined:
    Oct 31, 2009
    Messages:
    50
    Likes Received:
    0
    Loc:
    northern illinois
    I didnt get any kind of a certificate in the envelope
     
  9. Fsappo

    Fsappo
    Expand Collapse
    Minister of Fire

    Joined:
    Apr 9, 2008
    Messages:
    4,331
    Likes Received:
    180
    Loc:
    Central NY
    What certificate?
     
  10. new burner

    new burner
    Expand Collapse
    New Member

    Joined:
    Oct 31, 2009
    Messages:
    50
    Likes Received:
    0
    Loc:
    northern illinois
    whats the certificate say? tu tu sue
     
  11. tutu_sue

    tutu_sue
    Expand Collapse
    New Member

    Joined:
    Jan 21, 2006
    Messages:
    489
    Likes Received:
    0
    Loc:
    Northern NJ
    The baby's asleep in the room now. I'll have to wait until tomorrow to get it.
     
    Collapse Signature Expand Signature
  12. tutu_sue

    tutu_sue
    Expand Collapse
    New Member

    Joined:
    Jan 21, 2006
    Messages:
    489
    Likes Received:
    0
    Loc:
    Northern NJ
    Okay I scanned the certificate and the Hearthstone Quality Assurance Inspection Checklist. There was also the owner's manual and warranty registration but I didn't scan those. My stove was made in early 2006.
     

    Attached Files:

    Collapse Signature Expand Signature
  13. Highbeam

    Highbeam
    Expand Collapse
    Minister of Fire

    Joined:
    Dec 28, 2006
    Messages:
    11,130
    Likes Received:
    1,710
    Loc:
    Cascade Foothills, WA
    Funny to read the checklist.

    Things like bolts to pallet, cracks, leak test, etc. that are exactly what this thread is all about.
     
    Collapse Signature Expand Signature
  14. REF1

    REF1
    Expand Collapse
    Feeling the Heat

    Joined:
    Oct 13, 2009
    Messages:
    265
    Likes Received:
    0
    Loc:
    South West, VA
    I've learned quite a bit in reading this discussion. Fairly convinced me of a few things in my own situation.
     
    Collapse Signature Expand Signature
  15. new burner

    new burner
    Expand Collapse
    New Member

    Joined:
    Oct 31, 2009
    Messages:
    50
    Likes Received:
    0
    Loc:
    northern illinois
    I tood some more pictures in the attic, and I moved the insulation away from the pipe.
     

    Attached Files:

  16. emurphy@eclumber.com

    emurphy@eclumber.com
    Expand Collapse
    New Member

    Joined:
    Oct 19, 2009
    Messages:
    72
    Likes Received:
    0
    Loc:
    Southern NH
    They must have used a roof support. But they still should have framed the opening. And by now I'm sure you realize your missing the attic insulation shield, which, according to selkirk, is extremely important.

    Did you already post pics of the interior of the ceiling?
     
    Collapse Signature Expand Signature
  17. Fsappo

    Fsappo
    Expand Collapse
    Minister of Fire

    Joined:
    Apr 9, 2008
    Messages:
    4,331
    Likes Received:
    180
    Loc:
    Central NY
    Is the stove burning in the same room as the sleeping baby?!?
     
  18. new burner

    new burner
    Expand Collapse
    New Member

    Joined:
    Oct 31, 2009
    Messages:
    50
    Likes Received:
    0
    Loc:
    northern illinois
    This is what has been going on with my stove. Installers came back out yesterday and installed a new door handle and the heat shield.
    They took some pictures of the stove with thier phone. I told them that the chimney might be to short, that should be 8and a half feet tall(104'')
    They said it should be tall enough. They said it is over ten feet away from the roof , and it should be good. they said it is 5ft tall. I also asked why the chimney stove pipe going through the chimney is not framed out in the attic. They said only the square mount gets framed out not the round one.
    I also asked why the roof flashing was not flashed. They told me it was under the shingles, they said the top half of the flashing is about 10 inches longer, so ten inches of flashing is actually under the shingles. I will get up on the roof this weekend and check. As for the attic, well thats just crazy.
     
  19. new burner

    new burner
    Expand Collapse
    New Member

    Joined:
    Oct 31, 2009
    Messages:
    50
    Likes Received:
    0
    Loc:
    northern illinois
    I called the dealer while the installer were still at the house. I asked the dealer about the frameing in the attic, and a heat shield, and a insulation shield. He said he would look into it. I let him know I would be calling the inspectors out to look at it.
     
  20. branchburner

    branchburner
    Expand Collapse
    Minister of Fire

    Joined:
    Sep 27, 2008
    Messages:
    2,529
    Likes Received:
    284
    Loc:
    southern NH
    What are they saying about the stove itself: the leaking seams, and the braided rope gasket that indicates the stove was damaged and rebuilt?
     
    Collapse Signature Expand Signature
  21. new burner

    new burner
    Expand Collapse
    New Member

    Joined:
    Oct 31, 2009
    Messages:
    50
    Likes Received:
    0
    Loc:
    northern illinois
    I talked to the dealer again this morning, he said he talked with hearthstone and they are going to send some cement out to try and they will try and seal the stove. and put a different chimney cap on. And if that doesent work they will send out a new stove. Will see what happens, I have lost faith in these guys.
    I dont believe a word the dealer says. I dont think they know what they are doing.
     
  22. emurphy@eclumber.com

    emurphy@eclumber.com
    Expand Collapse
    New Member

    Joined:
    Oct 19, 2009
    Messages:
    72
    Likes Received:
    0
    Loc:
    Southern NH
    something has to be framed either the ceiling support or a roof support. Of course I just going be the directions on the selkirk website. Maybe there's another way, but that doesn't seem right. I would still get an inspector even if it was the fire dept. I'm sure they will come out for short change. probably even for free.
     
    Collapse Signature Expand Signature
  23. Fsappo

    Fsappo
    Expand Collapse
    Minister of Fire

    Joined:
    Apr 9, 2008
    Messages:
    4,331
    Likes Received:
    180
    Loc:
    Central NY
    Jeebus...cement? Tell them you want to job redone 100% right with a new stove or you will DEMAND 100% refund, them to remove their work and the house brought back to it's original condition. Do the You Tube video thing...publicity may be the only thing they listen to
     
  24. emurphy@eclumber.com

    emurphy@eclumber.com
    Expand Collapse
    New Member

    Joined:
    Oct 19, 2009
    Messages:
    72
    Likes Received:
    0
    Loc:
    Southern NH
    Unfortunetly we in the building material industry often see similar stuff happen. Anyone can sell a product, it's not until there is an issue, that you will test the salt of the dealer / retailer that you are doing business with. Publicity can do a couple of things. It will either cause them to be re-energized to fix the issue, or it will prevent another unsuspecting customer from having an issue that doesn't get fixed.

    Hope all turns out well.
     
    Collapse Signature Expand Signature
  25. new burner

    new burner
    Expand Collapse
    New Member

    Joined:
    Oct 31, 2009
    Messages:
    50
    Likes Received:
    0
    Loc:
    northern illinois
    branchburner,
    They dont seem to be taking it to seriuslly. I have been dealing with the owner of the store. He is the one that sold me the stove. I told him it seems as if someone tried to rebuild it. I wish he would come out and look at it. But I dont think they know what they are doing. I do have one more question for everyone though.
    The air wash system for the glass, my best guess would be that is the space in the front of the door, is that suppose to be be an open airway, or is it suppose to be sealed? On mine when I put my hand ontop of it, It is caulked, sealed shut. Is that how yours is?
     