ken999 said:
Weird as in 10 degrees difference from fittings to adjoining pipe sections. Got me...
OK, this is one of the limitations of an IR thermometer - it will read differently depending on the nature of the surface you are shooting, and it's responding differently to the PEX and the fittings. Some folks suggest putting strips of black electrical tape on the points you are measuring, and shooting the tape - it's supposed to give more consistent readings since the surfaces stay the same... Another thing that can make a big difference is the distance between the object and the gun - the "spot" that it measures is an angle, so the farther you are from the target, the bigger the spot and vice versa - on a relatively small and round object it can make a difference if you are far enough away to pick up the background as well as the thing being measured...
1 1/4" pex from the wall to an existing Hoval combination wood/oil boiler w/ 37 gallon domestic tank integrated. 40' or so...(house is 34' long, t-pex comes in the house on the opposite end of the basement from the Hoval.) My OWB is plumbed directly into the Hoval.
OK, so it sounds like what you are doing is a sort of hydraulic separator / Primary-Secondary variation where you have a primary loop going from the OWB to the Hoval and back, and then pull off the baseboards as a secondary loop - The layout makes more sense to me, though the temp numbers still don't, quite...
I've taken some more readings tonight and I get 178 supply temps at the foundation wall when the OWB bottoms out at 180. As far as I can tell I get 2-3 degrees drop from the OWB to the house IF the controller temp is right on the OWB. Or IF the IR reading is correct...lol...anyways I get around 5 degrees drop right there at the foundation wall...1 1/4" in, 1 1/4" out. 178 in from the OWB, 173 back out to the OWB.
Assuming that is right, figure 5°F drop for the round trip - acceptable but not great...
Now what I'm confused by, is it seems like you are hardly getting any drop across the Hoval - your prior seemed to say you were dropping a couple degrees running across the basement and back with the uninsulated PEX (not inherently bad since it's heat that you are finding useful) This suggests that either the numbers are wrong, or you are pushing so much water through the primary loop that the 152°F return from the secondary loop isn't mixing down the primary temp significantly... If so, it would suggest that you are way over-pumping the primary - ideally your secondary drop should be pulling most of the heat available in the primary - otherwise you are just wasting a lot of energy pushing BTU's around the primary loop...
Now, checking the 3/4" pex lines off the Hoval gets me 176-178 out, 152 or so back into the Hoval. The FF loop is fed by a 007 Taco. I'm not sure the total length of this loop but I could measure it if it will help. This is the 48' of baseboard on the FF that is in question. 25 or so degrees drop sounds to me like I'm stripping the heat off pretty good in this loop.
I would agree, it sounds to me like the the baseboard loop is doing about what it should... But if you are having trouble keeping the house warm on design day, this sounds like the problem area, where you don't have enough emitter to supply the needed BTU's.
I need to insulate the lines in the back of the OWB and I COULD try to insulate the 1 1/4" pex supply in the basement to tweak out the last degree or two, but it sounds like I'm not all that far off. I'd like to increase the FF baseboard to 60' or so to strip some more heat off in cold cold conditions (-20f).
Given the existing drop I would probably say not to add more BB to that loop, as I don't think you have the temperature to support it... Instead I would say to look at improving your insulation / weather sealing in order to cut down on the demand side, or look at adding additional loops of emission in parallel to the existing one... On general principles, I would say to consider lower temp emitters like retrofitting underfloor radiant, or panel radiators rather than BB, but that is a side issue.
Insulating the primary loop lines will no doubt help a small amount by reducing your drops there, but that doesn't seem to be your problem, the main issue seems to be a lack of emitter area... The reason it now seems inadequate is that with the old system, you had the heat losses from the Hoval warming your basement, and helping the BB - but you've now moved those losses outside with the OWB...
Bumping the OWB to 190 in a cold snap would likely help a bit too.[/quote]
Agreed, just because it would push the BB water temps up that much more, but again it doesn't seem to be the main issue...