Add-on Wood Boiler

Marshy Posted By Marshy, May 11, 2017 at 10:37 AM

  1. S.Whiplash

    S.Whiplash
    Member 2.
    NULL
    

    Oct 28, 2012
    80
    4
    Hate to break it to you but underground insulated pex at $8.50/ft. is either a very good deal or the quality is questionable. I would avoid the bubble wrapped pipe at any cost.
     
  2. Bad LP

    Bad LP
    Feeling the Heat 2.
    NULL
    

    Nov 28, 2014
    379
    124
    Loc:
    Northern Maine
    I'm 3 days into the installation. I'm doing the electric side in EMT and BX for the pumps running back into the generator panel while the 2 guys are doing the piping. Had to move the whole LP fired boiler arrangement around, remove prior wood stove, cut off manifolds and attach to a wall board, flue pipes, 2 300 gallon tanks, set the wood boiler on blocks to get it off the floor, set 2 300 ASME rated vertical gallon tanks on blocks to make room for insulation below them, double check then triple check the diagrams as we go, ect. ect.

    3 days in so far. 2 more to go.

    I think I want to puke at the cost of this project and doing it right. I don't know any other way than by the book.
    Not sure I'll live long enough for the pay back unless LP comes up to almost 4.00 a gallon again.
     
    Marshy likes this.
  3. NateB

    NateB
    Burning Hunk 2.
    NULL
    

    Mar 5, 2013
    202
    63
    Loc:
    South Central Pennsylvania
    Glycol is not necessary. The boiler will turn on its circulator pump if it gets too cold, and if your oil boiler is on that will keep it warm.

    Sent from my LG-D850 using Tapatalk
     
  4. Marshy

    Marshy
    Feeling the Heat 2.
    NULL
    

    Dec 29, 2016
    391
    86
    Loc:
    NY
    Again, another thing that I have barely begun to research. I just found a $8.5-10 cost per foot when cruising the forum. I plan to buy the appropriate stuff.

    The idea was to be able to shut down the boiler and walk away from it in the middle of winter if I was going to be away for a few days and not waste fuel oil on keeping the entire system warm. Rather, isolate the storage tank and wood boiler from the oil boiler and let the oil heat just like it's installed now.
     
  5. goosegunner

    goosegunner
    Minister of Fire 2.
    NULL
    

    Oct 15, 2009
    1,409
    103
    Loc:
    WI
    Have my Econoburn and storage in a remote shed that is insulated. My underground is buried below the frost line and both ends come up into heated space. We have traveled in the winter for 7-9 days with no problems. I heat the tank before we leave, shut off the pump to the house and turn on the electric base board in the boiler shed. The tank is usually still in the 145 range when we return.
     
  6. NateB

    NateB
    Burning Hunk 2.
    NULL
    

    Mar 5, 2013
    202
    63
    Loc:
    South Central Pennsylvania
    I would encourage you to try and get your storage into the basement. The oil to keep the boiler at 45f would not be that much.

    Sent from my LG-D850 using Tapatalk
     
    Marshy likes this.
  7. Marshy

    Marshy
    Feeling the Heat 2.
    NULL
    

    Dec 29, 2016
    391
    86
    Loc:
    NY
    That is my goal. I have the perfect place for the 820 gal tank in my basement.
     
  8. NateB

    NateB
    Burning Hunk 2.
    NULL
    

    Mar 5, 2013
    202
    63
    Loc:
    South Central Pennsylvania
    When you out that tank in make sure you have an inch or 2 insulation between the floor and any walls. Tom has some YouTube videos for installation

    Sent from my LG-D850 using Tapatalk
     
    Marshy likes this.
  9. JohnDolz

    JohnDolz
    Feeling the Heat 2.
    NULL
    

    Dec 29, 2015
    360
    41
    Loc:
    Burlington, CT
    I can share a few quick thoughts based on my experience. The guys here will tell you that I am a sales guy who has minimal data to support my thinking, just experience and gut feel:):

    1. This project will cost a lot more than you are estimating
    2. If you balance the size of the boiler with the storage everything else will take care of itself (i.e. if both are oversized it just means more time between fires - plus some heat loss since they are not in the actual house).
    3. I have a 60kw boiler that is rated at 205,000 BTU's and 1,000 gallon storage. Even when their is no call for heat (i.e. when I setback at night) my storage can absorb all of the energy produced as long as the top of my top tank is down in the low 150's or below.
    4. If you use Outdoor reset to mix your supply water you will get great efficiency and be able to run your tanks way down between firings. I have regular old baseboard that came with the house, regularly run my tanks down to under 120 and keep my house at 72 degrees. If you are interested there are a bunch of posts/discussions around this
    5. I try to minimize the # of fires so I let the tank temps drop way down and then just throw another 1/2 load of wood in at some point

    Hope this helps a bit.
     
  10. Marshy

    Marshy
    Feeling the Heat 2.
    NULL
    

    Dec 29, 2016
    391
    86
    Loc:
    NY
    All of that makes sense except I don't know what "outdoor reset" to mix the water supply means. Is that where you mix the returning water to keep the boiler return flow temp from going below 140? I will do some searching. I was thinking of purchasing Modern Hydronic Heating for Residential and Light Commercial Buildings by John Siegenthaler.
     
  11. maple1

    maple1
    Minister of Fire 2.
    NULL
    

    Sep 15, 2011
    7,440
    1,289
    Loc:
    Nova Scotia
    No, it's mixing on the distribution side that varies supply temps with outdoor temps. The aim being having constantly circulating water and even room temps by varying the supply temp.
     
    Marshy likes this.
  12. JohnDolz

    JohnDolz
    Feeling the Heat 2.
    NULL
    

    Dec 29, 2015
    360
    41
    Loc:
    Burlington, CT
    If you read John's PDF that is listed in the "Sticky Threads" you will see where he talks about using low temperature water. As part of that topic he talks about using emitters that are specifically designed for low temperature water. No doubt they would be better than standard baseboard but there would be a large price tag (for me) to swap out emitters. I have been able to heat my house to my desired temperature with the old baseboards by running an almost constant flow of low temperature water at a very low volume.

    Here is a link to a page that lists Outoor Reset devices that can complement any boiler/storage system. I do NOT have one of these (mine is build into my boiler controller) but one of the guys on Hearth recently installed one and was very pleased with his results:

    https://store.tarmusa.com/collections/mixing-valve-controllers
     
    Marshy likes this.
  13. Marshy

    Marshy
    Feeling the Heat 2.
    NULL
    

    Dec 29, 2016
    391
    86
    Loc:
    NY
    Thanks for the info. I envision this project evolving long term. I would like to incorporate all of those type of technologies but it might not be in the first year or two. I will make sure the system has the necessary hardware installed so I can plug and play with these different "adders". If the current baseboard heaters don't cut the mustard I can always add pex to the underside of my floors. That's just one option vs replacing my baseboard emitters or doing a low volume low temp circulation like you described.

    I have a lot to learn, I don't have a large background in controls but would like to think I'm a fast learner. Most of this is my first time being exposed to it.
     
    Highbeam likes this.
  14. JohnDolz

    JohnDolz
    Feeling the Heat 2.
    NULL
    

    Dec 29, 2015
    360
    41
    Loc:
    Burlington, CT
    No worries marshy. When I started this I could barely screw in a light bulb (I am not much beyond that now). I had someone install my system an I was planning to trust him infinitely. We had an upgrade to a bigger boiler planned after year 1 (long story) and sadly he passed away which left me with an undersized boiler in my house and an bugger size boiler sitting in a warehouse. Luckily the manufacturer in Sweden was awesome in helping me and I was forced to learn a few things along the way. Not sure where in NY you are but I am in Central CT, you are always welcome to come for a visit, see my layout if you think it might help you in your planning. Good luck!
     
    brenndatomu, Marshy and Highbeam like this.
  15. Marshy

    Marshy
    Feeling the Heat 2.
    NULL
    

    Dec 29, 2016
    391
    86
    Loc:
    NY
    OK, so I got a little help from @Chris Hoskin on a recommended boiler/storage tie to my existing system. I took what he gave me and drew my system and how it would interact with the boiler system. This is what I came up with...

    Only thing I'm unsure about is if I need the C1 circulator pump or not.

    Existing system is in black, in red would be new installation. IMG_20170604_180007181.jpg
     
  16. Marshy

    Marshy
    Feeling the Heat 2.
    NULL
    

    Dec 29, 2016
    391
    86
    Loc:
    NY
    If anyone is following, my diagram is drawn wrong. Don't use that.

    Anyways, I'll have time to get that straightened out while I wait for my boiler to come in. I bit the bullet and put a down payment on a Froling FHG 20/30. It will be paired with a 820 gallon American Solartechnics tank with a 100k BTU/hr htx.
     
  17. Highbeam

    Highbeam
    Minister of Fire 2.
    NULL
    

    Dec 28, 2006
    13,318
    2,451
    Loc:
    Mt. Rainier Foothills, WA
    Nice! Please document the project and costs. That's a great setup!
     
    Marshy likes this.
  18. NateB

    NateB
    Burning Hunk 2.
    NULL
    

    Mar 5, 2013
    202
    63
    Loc:
    South Central Pennsylvania
    I have a very similar setup to you, but I have and EKO 40 and I use primary secondary plumbing. I also bought a heat pump water heater from Tom. I recommend you tell Tom to through one on your skid before he ships it out. Are you going to do the plumbing yourself?
     
  19. Marshy

    Marshy
    Feeling the Heat 2.
    NULL
    

    Dec 29, 2016
    391
    86
    Loc:
    NY
    My existing hydronic system has an indirect 40 gallon DWH tank that I can use with the boiler/storage system and I have a GE Geospring stand-alone water heater that has been my primary for the last 3-4 years. I suspect that I will continue to use the GE through the summer when it makes less sense to fire the boiler. If I ever get solar I can heat the storage and maybe get rid of the GE.

    I plan to do the installation myself. I plan to construct a 8x12 insulated building detached from the house but within 30' of the storage.
     
  20. NateB

    NateB
    Burning Hunk 2.
    NULL
    

    Mar 5, 2013
    202
    63
    Loc:
    South Central Pennsylvania
    Make sure you get a good torch. I went with a cheap nozzle, and had leaks. bought a better torch, and it went much smoother.

    You can heat storage with the heat pump from Tom.

    I got the best price for fittings from supply house.

    Sent from my LG-D850 using Tapatalk
     
  21. Highbeam

    Highbeam
    Minister of Fire 2.
    NULL
    

    Dec 28, 2006
    13,318
    2,451
    Loc:
    Mt. Rainier Foothills, WA
    That heat pump from Tom. I would love to see a thread about the installation and hiccups. I have 1800 SF of slab with pex in it but no boiler, the heat pump would be perfect in my climate. Please????
     
  22. Fred61

    Fred61
    Minister of Fire 2.
    NULL
    

    Nov 26, 2008
    2,197
    426
    Loc:
    Southeastern Vt.
    Usually the first reason for leaks is prep of the surfaces. The second reason is not the nozzle so much but uneven heating of the joint. Directing the flame at one point, expecting the heat to conduct around the tubing will burn the Flux so the solder will not flow in that overheated area.

    Sent from my SM-G900R4 using Tapatalk
     
    Marshy likes this.
  23. NateB

    NateB
    Burning Hunk 2.
    NULL
    

    Mar 5, 2013
    202
    63
    Loc:
    South Central Pennsylvania
    I agree. My nozzle was so slow that I always had a cool spot, and the award location of the joints would make me rush and the result were poor. With the higher temperature I could get the joint up to temp and have the solder flow more quickly.

    I wish I could find some one to learn from, but everyone I know is to busy. Thanks for your tips. The guys on hear are always a great help.

    Sent from my LG-D850 using Tapatalk
     
  24. Marshy

    Marshy
    Feeling the Heat 2.
    NULL
    

    Dec 29, 2016
    391
    86
    Loc:
    NY
    The GE Geospring hot water heater is a stand alone heat pump/water heater. The heat pump that works similarly to a window air conditioner but rejects the heat into the water tank. It's not a ground thermal couple heat pump...

    Thanks for the tips on sweating. I don't have a ton of experience doing it but have some. I think I'll buy a nice little map gas torch.
     
  25. Fred61

    Fred61
    Minister of Fire 2.
    NULL
    

    Nov 26, 2008
    2,197
    426
    Loc:
    Southeastern Vt.
    Be careful with mapp. It's hot. Overheating will anneal the copper and shorten it's life. Not good especially at an ell where there's the most friction.

    Sent from my SM-G900R4 using Tapatalk
     