I could use some advice on how to document an alternate wall protection detail for a wood stove installation for my building inspector.
The stove manual calls for a min. clearance to combustibles of 10" for the stove and 13" for the stove pipe. The location of the rafter above the stove dictates that either the stove sits way out into the room, or that I slide the stove closer to the wall such that I end up with an 8" clearance from the back of the stove to the wall and 11-3/4" from the stove pipe to the wall.
The manual says "If an approved wall board is used this will reduce your clearance by two thirds (2/3); however a one inch (1") air space has to be between the board and the wall."
I was going to use the details shown on the Durock Submittal Sheet # 10310, but it states that the min. distance is 12".
So, what I would like to do is to fasten 1/2" of Micore 300 (R value 1.03) to the wall, then add 1/2" of Durock on top of that. I could use 2 layers of the Micore if needed.
I'm only reducing the stove clearance from 10" to 8", and the stove pipe clearance from 13" to 11-3/4" (measured to the face of the existing drywall).
Can it be documented that this would be OK?
Or would it be correct to just submit the USG cut sheet that states that Durock is non-combustible, and rely on the stove manual for the 2/3 reduction? (My reduction is only 1/5 as opposed to 2/3 - 20% vs. 67%, so I would think that this should be OK.)
Other options?
Thanks in advance for your advice!
Bill
The stove manual calls for a min. clearance to combustibles of 10" for the stove and 13" for the stove pipe. The location of the rafter above the stove dictates that either the stove sits way out into the room, or that I slide the stove closer to the wall such that I end up with an 8" clearance from the back of the stove to the wall and 11-3/4" from the stove pipe to the wall.
The manual says "If an approved wall board is used this will reduce your clearance by two thirds (2/3); however a one inch (1") air space has to be between the board and the wall."
I was going to use the details shown on the Durock Submittal Sheet # 10310, but it states that the min. distance is 12".
So, what I would like to do is to fasten 1/2" of Micore 300 (R value 1.03) to the wall, then add 1/2" of Durock on top of that. I could use 2 layers of the Micore if needed.
I'm only reducing the stove clearance from 10" to 8", and the stove pipe clearance from 13" to 11-3/4" (measured to the face of the existing drywall).
Can it be documented that this would be OK?
Or would it be correct to just submit the USG cut sheet that states that Durock is non-combustible, and rely on the stove manual for the 2/3 reduction? (My reduction is only 1/5 as opposed to 2/3 - 20% vs. 67%, so I would think that this should be OK.)
Other options?
Thanks in advance for your advice!
Bill