You can't use that black pipe elbow it needs to be stainlessI got a Lennox c210 and wanting to make sure I am safely attaching the insert to liner. I am new to wood stove life and wanting to do it right the first time. Thanks
View attachment 266813
great to know- also the round cast iron flange from top of stove to that black pipe doesn't bolt into place- am I good to hi temp silicone it to stove?You can't use that black pipe elbow it needs to be stainless
Nope. Not high enough temp and mechanical fasteners are requiredgreat to know- also the round cast iron flange from top of stove to that black pipe doesn't bolt into place- am I good to hi temp silicone it to stove?
Thanks a ton- looks like I'm way over my skis with this situationNope. Not high enough temp and mechanical fasteners are required
I cannot believe how much is involved in these inserts and their install, not to mention how expensive liners and liner insulation is!!Thanks
Thanks a ton- looks like I'm way over my skis with this situation
Good job on going with insulationI cannot believe how much is involved in these inserts and their install, not to mention how expensive liners and liner insulation is!!
I actually didn't could only afford liner... does insulation make a huge difference?Good job on going with insulation
So how are you hooking it up?I actually didn't could only afford liner... does insulation make a huge difference?
I was going to hook it up with the insert boot adapter: then to that positive flue connector ring/kit and use furnace cement to seal. I need to find that ring kit. I got excited by a good deal so I thought on a used insert with surround w/ blower and liner and now I really need to decide if I want to go through with it or maybe just repost to sell on craigslistSo how are you hooking it up?
Yes it does. It is also almost always required by code
What size is your flue? And does it have the required clearancesI was going to hook it up with the insert boot adapter: then to that positive flue connector ring/kit and use furnace cement to seal. I need to find that ring kit. I got excited by a good deal so I thought on a used insert with surround w/ blower and liner and now I really need to decide if I want to go through with it or maybe just repost to sell on craigslist
I seriously doubt a fireplace flue is 8x8. Chimneys for use with woodburning appliances need for an internal chimney 2" from the outside of the masonry chimney to combustible materials. For external ones it is 1"think flue is an 8"x8" and liner is 6" round, not sure about required clearances...
That is way to large the flue gasses will expand quickly causing cooling which will create creosote and severely compromise draftit's about 13" x 13" on exterior edges, so guess you're probably right, must be bigger than 8 x 8
Thanks it'll be close the liner it came with is 12' long and real close to being long enough- I might also be able to use a 1 foot long straight stainless pipe just in case as I guess the black doesn't handle as high of heat. I need to get a different collar that can be fastened to stove as the one that came with the used insert can't be fastened only silicone-d. Guess I also need to look into insulating the liner...What you have pictured is a correct option, but make sure that for your installation you need the elbow. If the alignment is good you might be able to take the liner right down to that appliance adapter and into the flue collar with no elbow. That will save a bit. Screw through the flue collar into the appliance adapter with 3/4" sheet metal screws.
PUMPED- Found a positive flue connector kit at Hearth & Grill Sales LLC out of Tennesee!!So as of now- looks like I need to order insulation for liner which I found a place that has 15' long as well as a place that does 5' & 10 foot sections- my liner is 12' so no need to pay for 25' I am also amazed by how elusive a positive flue connector ring kit (part #71161) is to find for Ironstrike/Lennox c210 insert, still trying to find a place that has one in stock!!
Ok that doesn't change the fact that the flue is way to large. Have you even had atleast a level 2 inspection done on the flue?PUMPED- Found a positive flue connector kit at Hearth & Grill Sales LLC out of Tennesee!!
What is currently on the stove in the picture that you posted. It looks like a flue collar.I am also amazed by how elusive a positive flue connector ring kit (part #71161) is to find for Ironstrike/Lennox c210 insert, still trying to find a place that has one in stock!!
It is a flue collar but it is one for a Buck stove and doesn’t mechanically attach to the stove- would have to like silicone it or something. This used stove process is like an onion keep peeling away the layers.,,What is currently on the stove in the picture that you posted. It looks like a flue collar.
no inspection yet- aren’t I good if I get 1/2 “insulation- wrap liner and install- 6 “ liner with another 1” of insulation??Ok that doesn't change the fact that the flue is way to large. Have you even had atleast a level 2 inspection done on the flue?