Chimney for pellet stove

gguy Posted By gguy, May 27, 2018 at 7:01 AM

  1. gguy

    gguy
    New Member 2.
    NULL
    

    May 27, 2018
    5
    0
    Loc:
    new jersey
    Hi everyone. I have a quick question about venting my soon to be new pellet stove. I tore out my prefab fireplace last week and am buying a harman accentra insert. The old chimney came right out but there's still a 8" lining running up to the top of my roof. i plan on running 4" vent pipe right through this. I assume I have to have a seal of some sort at the bottom and maybe top of this 8" liner. My question is what would I use to seal this?
     
  2. gguy

    gguy
    New Member 2.
    NULL
    

    May 27, 2018
    5
    0
    Loc:
    new jersey
    Well I just measured it and its a 11" liner not 8. I guess I have will have to make something.
     
  3. johneh

    johneh
    Minister of Fire 2.
    NULL
    

    Dec 19, 2009
    1,589
    626
    Loc:
    Eastern Ontario
    Is that a liner that went up the inside of a masonry chimney ?
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  4. gguy

    gguy
    New Member 2.
    NULL
    

    May 27, 2018
    5
    0
    Loc:
    new jersey
    No it’s a fake wooden chimney on the side of my house. Framed out with 2x4s. The main chimney for the prefab fire place was a 6 in double wall that came out when I removed the fire place. Then there’s a 11 in thin metal sleeve going up to the roof
     
  5. johneh

    johneh
    Minister of Fire 2.
    NULL
    

    Dec 19, 2009
    1,589
    626
    Loc:
    Eastern Ontario
    Then it just a chase OK
    Block off both ends and seal
    Run the smoke pipe straight out
    Save a bundle of money on pipe
    If you can
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  6. mralias

    mralias
    Minister of Fire 2.
    NULL
    

    Apr 29, 2008
    1,095
    255
    Loc:
    MA
    And if you don't want to do it the easy way as johneh mentioned, how far of a run is it to the top. It matters as anything over 15 feet you may have to go to 4" which is much more money.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  7. gguy

    gguy
    New Member 2.
    NULL
    

    May 27, 2018
    5
    0
    Loc:
    new jersey
    Thanks guys. I was initially gonna go through the wall but there a giant bush type tree on the other side my wife loves. So I wouldent have clearances for the chimney. It’s only a 15’run up the chimney. I will block off both the top and bottoms and probably run 4”. Now my problem is trying to connect straight pipe to the Harman Accentra 52i. Everyone seems to use flex which I can’t use.
     
  8. gguy

    gguy
    New Member 2.
    NULL
    

    May 27, 2018
    5
    0
    Loc:
    new jersey
    ok complete change of plans. Screw the bush its coming down. I want to now run the chimney through the wall like johneh mentioned. Much cheaper and easier. Now heres another issue. I have a harmon insert that im installing flush against the wall. the double wall pipe will technical be in a enclosed space in the chase correct? It will be coming up and out of a zero Clarence box before making a 90 and straight out the wall. not that i have permits or anything but when the day the comes that we need to sell the house I would like it to pass a inspection.
     
  9. mralias

    mralias
    Minister of Fire 2.
    NULL
    

    Apr 29, 2008
    1,095
    255
    Loc:
    MA

    Better check that manual about that one. I would be more concerned that if something happened and a fire started that the insurance company is not going to deny your claim because it was not install to code and a permit was pulled and install was inspected. Better safe than sorry.
     