I cleaned our chimney last month and found cracked ceramic flue tile at the thimble. Apparently we had a chimney fire without realizing it, and need to get it repaired in the next month or two. Brick chimney, 6.5" x 10" i.d. tile, 24' high from slab to chimney cap, 20' thimble to cap. Phoenix hearthstone woodstove w/6" pipe transitioning to 8" thimble. Cleaned yearly with a tight-fitting wire brush.
A chimney sweep recommended by a trusted local mason quoted $2875 for a 5.5" uninsulated steel liner. The tech said that the undersize liner would avoid any installation issues if the flue tiles were offset (they don't appear to be) and the air space around it would give sufficient insulation.
Another outfit came back with this:
"For roof access, flue knockout, and installation of an insulated stainless steel smooth inner wall liner = $5,275-$5,575 (depending on the length of the tail to the clean out door).
We entertained ovalizing the liner to fit within the existing clay flue tile. Given the glazed creosote in the existing flue we advise against that tactic as the heat radiating from the liner will liquefy the creosote and cause other problems like leeching and odor. "
I assume "flue knockout" means they would bust up the flue liner and remove it through the cleanout door to provide adequate clearance for the new insulated liner.
What do you recommend? I want to do this right and only once. Would a 5.5 " liner provide adequate draft? Is it likely to cause more problems with the existing tile than we had without the liner (basically none)? Do I need an insulated liner?
A chimney sweep recommended by a trusted local mason quoted $2875 for a 5.5" uninsulated steel liner. The tech said that the undersize liner would avoid any installation issues if the flue tiles were offset (they don't appear to be) and the air space around it would give sufficient insulation.
Another outfit came back with this:
"For roof access, flue knockout, and installation of an insulated stainless steel smooth inner wall liner = $5,275-$5,575 (depending on the length of the tail to the clean out door).
We entertained ovalizing the liner to fit within the existing clay flue tile. Given the glazed creosote in the existing flue we advise against that tactic as the heat radiating from the liner will liquefy the creosote and cause other problems like leeching and odor. "
I assume "flue knockout" means they would bust up the flue liner and remove it through the cleanout door to provide adequate clearance for the new insulated liner.
What do you recommend? I want to do this right and only once. Would a 5.5 " liner provide adequate draft? Is it likely to cause more problems with the existing tile than we had without the liner (basically none)? Do I need an insulated liner?