Northern Heat said:
The boiler as told by econoburn does not need a mixing valve as it never lets the water get below 154 degrees except at start up when the first loads of water return from the slab.So far it has worked great. Though the proof is in the pudding and only time will tell.
One thing I did today was up the goal temp for the boiler to 165 and that even made a big difference in the creasote build up as it did idle less.Maybe I will bring it up more perhaps 170 would clear up things even more. What temp do you run at? One thing I am worried about is shocking the cement pad but so far no cracking at all,of coarse it never gets above 26 celcius/78 f. The idling is probably the biggest culprit, as my boiler idles 1/3 of the time,or more, once the first few load of heat go to the slab.Like you say storage will make the biggest difference.
Thanks to DON"T PANIC for the creasote info on the harder higher btu woods.We do have a fair amount of birch up here and I cut a lot of it already as I use it for wood turning.Too bad the boiler isn't designed for wood shavings.
I have been reading this boiler forum for about six months and have read a fair amount of what you guys have written.It has all been fairly helpful in the set up of my system. A great resource !!
That 154 is possibly a bit misleading, as it may just be the overall boiler temperature, not the actual temperature of the water entering the boiler right at the return fitting - This is the temp that really matters, as if you have low return temp problems, it's where the damage will occur... Do you actually have a way of monitoring the temp on that return pipe?
Running up the boiler temp will reduce idling, but it does have the potential issue of reducing the margin between the temp where the boiler will go into idle, and when it hits an overtemp event... Often the temp will go up a little after going into idle, so this can sometimes be a problem, but not necessarily... The other thing is it will slightly reduce your efficiency, and increase your wood consumption... The boiler will transfer heat into the water most efficiently when the water is entering the boiler at the lowest possible non-condensing temperature. Raising the boiler target temp cuts into this a bit. Also the higher the boiler temp, the faster the boiler itself will radiate heat to the outside and cool... (This is mostly a concern w/ outbuilding installs, heat radiated from an inside install still warms the house, but it's still a question as to whether you need the added heat in the boiler room)
Everybody's goal temperature varies a bit, depending on the details of their load setup, whether they have storage, and so forth... It is one of those things that you have to experiment with a bit to find your best value in your house...
In terms of the temps going into the slab, it is your call, but I really wouldn't advise pushing excessively hot water into the slab - the experts have a suggested limit, and I figure there is a good reason for it - including looking at the long term slab life...
Lastly, the docs on most of the boilers that I've read seem to say that you CAN burn untreated / painted shavings, sawdust and other processing scraps as long as you keep the amounts reasonable and mix it in with cord wood... Certainly it makes fantastic fire starter, and many people say that it is great in cold weather for getting the boiler up to temp in a hurry... The two main approaches I've seen suggested are to either load part way with cordwood and then add a few scoops of shavings followed by more cordwood, etc. or to pack the shavings tightly into a paper bag and put that in with a bunch of other wood. Either way it puts out a lot of heat when you do this, so I'd save most of the shavings until your peak demand season...