Dropped off stove, vent pipe, and floor protector docs at city hall, filled out a permit application a few days ago - the inspector will be in Monday. I didn't need to submit a drawing/description of the installation.
Manual and sticker on back of the stove say single wall pipe can be 10" from the wall in USA. I contacted Drolet and they said this is only if I use approved shielding, which I'll do - their pipe (SP00370) and shield (SP00390). Pipe manual says with "approved shielding" single wall clearance can be reduced by 67% (think I read 50% elsewhere), which would be 6" - mine will be ~12" from the wall.
1) Should this be okay or might the inspector want proof of testing, etc? My neighbor said inspectors don't care about shielding.. that they go by non-shielded specs (though he may have meant wall shielding for stove clearance).
I'm using a basic floor protector (HY-C T2UL3648GT-1C) that will extend 10.25" on each side of door opening (USA spec is 8"), 19" from door opening/18" from glass (USA spec is 16"), and 3.75" from back of stove (USA spec is 0"). Drolet manual only says use Type 2 - has no r-value, thickness spec.
2) Should this be okay, or can local code be different?
The stove is placed in front of a 32" wide return duct (a 64" wide return is ~12 ft away in the hall) - both are near the ceiling. The manual says "The wood stove must not be hooked up to a hot air distribution system since an excessive accumulation of heat may occur" (not sure what this means), but there's much on inet about people wanting to pull wood stove heat into return ducts (effectiveness debatable). The Legend's fan only blows heat up from the back of the stove (there's a lip at top of rear heat shield that directs it slightly away from wall) so blown heat will go toward the return.
3) Is this stove too close to the return duct?
Concern is that the inspector will sign off the permit, but then say he doesn't like something when he checks it (even though it meets stove specs) and I'll have to change it. Replacing the SWP with double wall is easy, replacing the hearth pad would be wasted time/effort, but having to move stove placement would be bad (chimney pipe goes straight up - I don't want bends). I don't want to count on him saying "Well I'd like to see 'such and such', but it meets mfgr's USA spec so I'll pass it". I didn't see much about wood stove installation in local code (only that chimneys up side of house have to be supported, etc and covered to match house exterior).
4) Should I submit a drawing (take one when I pick up the permit), try to talk to the inspector, etc?
Any suggestions about this install will be appreciated.
I have questions about TV distance from stove, how far tree limbs should be from the chimney opening, and if local code might require a roof chase to cover the stainless steel chimney, but they're secondary.
Dropped off stove, vent pipe, and floor protector docs at city hall, filled out a permit application a few days ago - the inspector will be in Monday. I didn't need to submit a drawing/description of the installation.
Manual and sticker on back of the stove say single wall pipe can be 10" from the wall in USA. I contacted Drolet and they said this is only if I use approved shielding, which I'll do - their pipe (SP00370) and shield (SP00390). Pipe manual says with "approved shielding" single wall clearance can be reduced by 67% (think I read 50% elsewhere), which would be 6" - mine will be ~12" from the wall.
1) Should this be okay or might the inspector want proof of testing, etc? My neighbor said inspectors don't care about shielding.. that they go by non-shielded specs (though he may have meant wall shielding for stove clearance).
I'm using a basic floor protector (HY-C T2UL3648GT-1C) that will extend 10.25" on each side of door opening (USA spec is 8"), 19" from door opening/18" from glass (USA spec is 16"), and 3.75" from back of stove (USA spec is 0"). Drolet manual only says use Type 2 - has no r-value, thickness spec.
2) Should this be okay, or can local code be different?
The stove is placed in front of a 32" wide return duct (a 64" wide return is ~12 ft away in the hall) - both are near the ceiling. The manual says "The wood stove must not be hooked up to a hot air distribution system since an excessive accumulation of heat may occur" (not sure what this means), but there's much on inet about people wanting to pull wood stove heat into return ducts (effectiveness debatable). The Legend's fan only blows heat up from the back of the stove (there's a lip at top of rear heat shield that directs it slightly away from wall) so blown heat will go toward the return.
3) Is this stove too close to the return duct?
Concern is that the inspector will sign off the permit, but then say he doesn't like something when he checks it (even though it meets stove specs) and I'll have to change it. Replacing the SWP with double wall is easy, replacing the hearth pad would be wasted time/effort, but having to move stove placement would be bad (chimney pipe goes straight up - I don't want bends). I don't want to count on him saying "Well I'd like to see 'such and such', but it meets mfgr's USA spec so I'll pass it". I didn't see much about wood stove installation in local code (only that chimneys up side of house have to be supported, etc and covered to match house exterior).
4) Should I submit a drawing (take one when I pick up the permit), try to talk to the inspector, etc?
Any suggestions about this install will be appreciated.