Gasification boiler thoughts

woodboilerwonder Posted By woodboilerwonder, Aug 6, 2019 at 8:45 PM

?

wood gasification pressurized boiler or traditional wood boiler

  1. wood gasification pressurized

    3 vote(s)
    100.0%
  2. traditional boiler

    0 vote(s)
    0.0%
  1. woodboilerwonder

    woodboilerwonder
    New Member 2.
    NULL
    

    Aug 6, 2019
    6
    0
    Loc:
    Missouri
    Hello, I am considering a wood gasification boiler. I believe I want a pressure boiler. I have a basic knowledge of wood heat and water heat boiler systems but no wood boiler experience. I was excited about getting a used eko 80 boiler. Burning less wood is intriguing but reading about people having trouble getting the gasification to work concerns me. I wouldn't mind fiddling with it a bit but after the initial learning i would hope to just fill it with wood once or twice a day and forget about it. I did some reading and it looks like the units are pretty particular on what wood is burned in them. I was thinking I would burn hedge and or oak half of the time and used pallets or soft maple half of the time. Neighbors are 6-800 feet away and the stove would also be that far from my house. Will this mix of good wood and junk render the unit terribly inefficient and or lead to continual maintenance?
     
  2. hondaracer2oo4

    hondaracer2oo4
    Feeling the Heat 2.
    NULL
    

    Jan 18, 2012
    412
    63
    Loc:
    Canterbury NH
    Are you looking at just Indoor model stuff? There are a couple extremely efficient owb gassers on the market that are very simple to run and are not finiky. They are nothing like the owb people think of in the past. They are well built, have real warranties that the companies stand behind and are phase two epa qualified. Atleast put some thought and time into looking at the Heatmaster G series.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  3. E Yoder

    E Yoder
    Feeling the Heat 2.
    NULL
    

    Jan 27, 2017
    288
    45
    Loc:
    Floyd, VA
    6-800' distance from the boiler to the house? That's way out there. Flow rates will be pretty low.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
    Highbeam likes this.
  4. maple1

    maple1
    Minister of Fire 2.
    NULL
    

    Sep 15, 2011
    9,853
    2,077
    Loc:
    Nova Scotia
    My thoughts also.

    Think there is a lot more homework required aside from the original questions.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  5. salecker

    salecker
    Minister of Fire 2.
    NULL
    

    Aug 22, 2010
    928
    289
    Loc:
    Northern Canada
    A pressurized water jacket = boiler
    unpressurized water jacket= water heater
    Gasification requires wood that is seasoned and dry.
    Green wood contains water,which is what firefighters use to put out fires.Dosn't really work efficiently for emitting heat and will cause you nothing but headache in a gasifyer.
    Don't try for one that does everything,they don't exist.
    if you go gasifyer,do so realizing wood quality is important,don't lie to yourself.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  6. Bad LP

    Bad LP
    Minister of Fire 2.
    NULL
    

    Nov 28, 2014
    856
    308
    Loc:
    Northern Maine
    Just the PEX is going to cost a fortune!!!!
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  7. hondaracer2oo4

    hondaracer2oo4
    Feeling the Heat 2.
    NULL
    

    Jan 18, 2012
    412
    63
    Loc:
    Canterbury NH
    Wow. I missed the 600 feet part! Why would someone do that?
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  8. Medic21

    Medic21
    Feeling the Heat 2.
    NULL
    

    Feb 26, 2017
    468
    365
    Loc:
    Northern Indiana
    800 x $15 = $12000

    Almost equal cost to the boiler. Would be a deal breaker for me. Take 20 years on a $30k install for return on investment. Just in time to replace the unit.


    Sent from my iPhone using Tapatalk
     
  9. 3fordasho

    3fordasho
    Minister of Fire 2.
    NULL
    

    Jul 20, 2007
    805
    213
    Loc:
    South Central Minnesota
    Not to mention the pex diameter required to get usable flow rates. 1" might not do it :rolleyes:
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
    brenndatomu likes this.
  10. brenndatomu

    brenndatomu
    Minister of Fire 2.
    NULL
    

    Aug 21, 2013
    3,992
    1,459
    Loc:
    NE Ohio
    Yeah at that point it would have to be an indoor model, or nothing...
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  11. woodboilerwonder

    woodboilerwonder
    New Member 2.
    NULL
    

    Aug 6, 2019
    6
    0
    Loc:
    Missouri
    Thanks guys! I also have a second small house and a future pool i want to heat. The 800 feet is the distance between the 2 houses. Maybe i should put it in the middle and run smaller pex 2 directions. My wife will only bless this plan if she, "almost" never smells the smoke! What should I ask for pictures of on an eko80 to know if it is in good shape? It's about 10 years old and has been used inside a large building that is a cabinet shop. I am thinking of asking for pictures now and then if they look good go look at it. I assume I can pressurize it with an air bubble to see if it leaks. I am ok with some risk that comes with buying a used item as long as simply moving the stove does not present likely damage.
     
  12. maple1

    maple1
    Minister of Fire 2.
    NULL
    

    Sep 15, 2011
    9,853
    2,077
    Loc:
    Nova Scotia
    I would not recommend this.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  13. brenndatomu

    brenndatomu
    Minister of Fire 2.
    NULL
    

    Aug 21, 2013
    3,992
    1,459
    Loc:
    NE Ohio
    Still gonna have a bazillion dollars in the pipe...cause it still totals 800 ft.
    And don't skimp on the underground pipe, you WILL be sorry later...
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  14. woodboilerwonder

    woodboilerwonder
    New Member 2.
    NULL
    

    Aug 6, 2019
    6
    0
    Loc:
    Missouri
    I was thinking wrong above on the distance. I was thinking round trip distance. 1 inch oxygen barrier pex is 66 cents per foot. It's about 375 feet one way. If i do paralleled run of this pipe it's 375 x 4 x .66 per foot. This is $990.00 plus the foam in ditch method I have read about on this site and fittings I suppose. Hopefully I can find it in a roll that won't have to have a splice.
     
  15. woodboilerwonder

    woodboilerwonder
    New Member 2.
    NULL
    

    Aug 6, 2019
    6
    0
    Loc:
    Missouri
    Would not recommend pressurizing the boiler or doing the project?
     
  16. brenndatomu

    brenndatomu
    Minister of Fire 2.
    NULL
    

    Aug 21, 2013
    3,992
    1,459
    Loc:
    NE Ohio
    375 to each house? That's not much different than before. And that much foam will still not be cheap either...
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  17. maple1

    maple1
    Minister of Fire 2.
    NULL
    

    Sep 15, 2011
    9,853
    2,077
    Loc:
    Nova Scotia
    The project.

    Mainly based on the 800' distance.

    If it is rather 400' (is that the actual distance between the houses? still not sure...), I still would have second thoughts.

    For starters - base your piping costs on 1-1/4" pipe. Not 1". And run some numbers, or get someone who knows how to do that (there are those on here who can), on what is involved in pumping all that heat through all that pipe all that distance. (A decent calc would also need to know your heat load or how much heat your heated spaces will need). That might even reveal that you might need 1-1/2" pipe. And the size/number of pumps needed will also be pricey.

    You would also need to put an Eko 80 in a building of some sort. Preferably one that can utilize the standby heat loss. And maybe also big enough to hold your winters wood. Storage would also be preferable - you could maybe put some tanks in the houses for that.

    That's not touching yet on your existing system and what you would need to do to adapt this to that.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
    TCaldwell likes this.
  18. woodboilerwonder

    woodboilerwonder
    New Member 2.
    NULL
    

    Aug 6, 2019
    6
    0
    Loc:
    Missouri
    It is 375 feet between the houses. The ideal place for the stove is near or in the smaller house. It has a 2 car garage and i was thinking of putting the stove and 2 1000 gallon propane tanks for pressurized storage into one of the garages. On the one inch pex I was saying I could run 2 supply and 2 return 1 inch lines. A little googling says this is the pressure drop and pump sizing etc. I take 500 x 5 gpm x 20 deg temp drop equals 50,000 btu transferred. I was going to run 2 of these circuits paralleled so it would be 100,000 btu.
    I looked at technical document td10 about how to size a circulator and If I did it right an 007 on each of the 2 paralelled circuits would work. I was coming up with 14 feet of head. Please correct me here I am taking a stab at this but realize I likely made a mistake or more likely mistakes.....
     
  19. maple1

    maple1
    Minister of Fire 2.
    NULL
    

    Sep 15, 2011
    9,853
    2,077
    Loc:
    Nova Scotia
    375 feet one way is 750 feet total loop. I took a quick look at the first table I googled up and came up with in the area of 26' of head at 5gpm and 160° for 1" pex.

    That's not accounting for anything else presenting head, like fittings & exchangers.

    Chart for a 007 I think shows head topping out around 8', at 5gpm, going to zero flow at just over 10' of head.

    I'm not saying what you want to do isn't dooable - but there a lot of things to consider.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  20. E Yoder

    E Yoder
    Feeling the Heat 2.
    NULL
    

    Jan 27, 2017
    288
    45
    Loc:
    Floyd, VA
    A 009 perhaps? 007 would be dead in the water at that distance (my experience).
     