    New to the forum and figured i can ask if anybody has info on this Gatling stove. Need the specs and clearances thanks
     

    Attached Files:

  2. bholler

    bholler
    Minister of Fire 2.
    NULL
    

    Jan 14, 2014
    11,069
    2,071
    Loc:
    central pa
    Clearances are 36" to combustibles. What is behind the brick on the walls?
     
  3. Brian279

    Brian279
    New Member 2.
    NULL
    

    Dec 6, 2017
    9
    0
    Loc:
    Va
    Sorry thats was a pic of the stove im picking up...i wish i had a brick wall..this ia what i have now.. Behind that paneling is a square chimney. Can not find a clean out so im gueasing its behind the paneling. House is on a slab so im gonna cut the carpet between the blue lines and lay ceramic tile and build a heat shield on the wall. Alot of work and its getting cold
     

    Attached Files:

  4. Brian279

    Brian279
    New Member 2.
    NULL
    

    Dec 6, 2017
    9
    0
    Loc:
    Va
    Coming out the roof its the big square chimney block with red clay flue liners. Just bought this house. And never seen a chimney built like this.. Any insight on this. Is this chimney for wood or gas???.
    Also waiting on a guy to inspect and clean it
     
  5. bholler

    bholler
    Minister of Fire 2.
    NULL
    

    Jan 14, 2014
    11,069
    2,071
    Loc:
    central pa
    That sounds like a pretty standard chimney to me. You can reduce the clearances to 12" with a proper ventilated heat sheild. But you also need to deal with the wall passthrough you need 12" of solid masonry going through the wall. You also need clearance from the outside of the masonry chimney.
     
  6. Brian279

    Brian279
    New Member 2.
    NULL
    

    Dec 6, 2017
    9
    0
    Loc:
    Va
    Im going by what existing from the 70's.
    Everything looks good looking in to the chimney from the opening but still want to get it inspected. My biggest concern was the clearence and heat shield.
    Do you think there is a cleanout somewhere or did the not install them on some
     
  7. bholler

    bholler
    Minister of Fire 2.
    NULL
    

    Jan 14, 2014
    11,069
    2,071
    Loc:
    central pa
    No it does not look good the paneling is way to close to the pipe going through the wall. And there are plenty of chimneys with no cleanout.
     
  8. Brian279

    Brian279
    New Member 2.
    NULL
    

    Dec 6, 2017
    9
    0
    Loc:
    Va
    This how it is/was when i brought the house
     

    Attached Files:

  9. bholler

    bholler
    Minister of Fire 2.
    NULL
    

    Jan 14, 2014
    11,069
    2,071
    Loc:
    central pa
    Yes it is unsafe
     
  10. Brian279

    Brian279
    New Member 2.
    NULL
    

    Dec 6, 2017
    9
    0
    Loc:
    Va
    What do i need to change or do? Want this this safe and right before i fire it up. Im not in a hurry by no means . i do have central air and heat but dont like the high heat bills
     
  11. bholler

    bholler
    Minister of Fire 2.
    NULL
    

    Jan 14, 2014
    11,069
    2,071
    Loc:
    central pa
    Either cut it back and put in 12" of solid masonry on all sides of the crock or get an insulated wall passthrough
     
  12. Brian279

    Brian279
    New Member 2.
    NULL
    

    Dec 6, 2017
    9
    0
    Loc:
    Va
    One of these
     

    Attached Files:

  13. bholler

    bholler
    Minister of Fire 2.
    NULL
    

    Jan 14, 2014
    11,069
    2,071
    Loc:
    central pa
    Yes that is actually the one we use. It is the easiest one we have found to install.
     
  14. Brian279

    Brian279
    New Member 2.
    NULL
    

    Dec 6, 2017
    9
    0
    Loc:
    Va
    So the will screw into where my old one is and the other end will slide into the chimney... Basically plug and play or?
     
  15. bholler

    bholler
    Minister of Fire 2.
    NULL
    

    Jan 14, 2014
    11,069
    2,071
    Loc:
    central pa
    No it screws fast to the chimney. You need to cut back all of the flammables.
     
  16. Brian279

    Brian279
    New Member 2.
    NULL
    

    Dec 6, 2017
    9
    0
    Loc:
    Va
    Should be easy enough for a weekend project. Now for the heat shield. I have seen many diffrent ways other people has done theirs. Any insight of the way you would do it on the panel wall. I no i would love to tear the panel down and brick it but aint no telling all i would get it to doing that
     
  17. bholler

    bholler
    Minister of Fire 2.
    NULL
    

    Jan 14, 2014
    11,069
    2,071
    Loc:
    central pa
    Any non combustible material spaced off the wall with noncombustible spacers. And a 1" gap top and bottom to allow for airflow.
     