Hello again.
I am really driving myself crazy here to ensure I am SET for install.
The insert is being put into an existing masonry fireplace. The hearth is about 19" deep and is level with the carpet floor.
The stove doors will stick out 9 inches and the bottom lip 11".
This gives me a minimum of 8 inches of existing hearth in front for protection, which I know is not code.
The manual states this:
Floor protection must be non-combustible, insulating material with an R value of
1.1 or greater.
* Hearth thickness of 0.5" with k value = 0.84", R value = 6 or greater.
Thermal floor protection is not required if the unit is raised 3.5" minimum (measured
from the bottom of the stove). However, standard ember floor protection is required.
It will need to be a non-combustible material that covers 16" (406 mm) in the US and
18" (450 mm) in Canada to the front of the unit and 8" (200 mm) to the sides.
If the unit is not raised, thermal floor protection required is 18" (450 mm) in the
US and Canada.
All floor protection must be non-combustible (i.e., metals, brick, stone, mineral
fi ber boards, etc.) Any organic materials (i.e. plastics, wood paper products, etc.)
are combustible and must not be used. The floor protection specified includes
some form of thermal designation such as R-value (thermal resistance) or k-factor
(thermal conductivity).
The fire prevention guy for the town said I pretty much just need spark protection, even a hearth rug. I think not......
So, a mason is going to install about an additional foot more of hearth (flush to the floor in front of the existing hearth). By removing carpet, adding some type of backer board and tile or stone as the top layer. The stone will be continued over the brick for continuity.
From what I read here, it seems ok but this R value stuff baffles me! I guess it might come down to the raised 3.5" requirement. Does the existing built in hearth = raised the depth of a brick plus the concrete or does it not count because that same hearth is floor level??
Does this meet the manual requirements to cover me in case of incident?
Thanks in advance!
Nervous Nellie!
I am really driving myself crazy here to ensure I am SET for install.
The insert is being put into an existing masonry fireplace. The hearth is about 19" deep and is level with the carpet floor.
The stove doors will stick out 9 inches and the bottom lip 11".
This gives me a minimum of 8 inches of existing hearth in front for protection, which I know is not code.
The manual states this:
Floor protection must be non-combustible, insulating material with an R value of
1.1 or greater.
* Hearth thickness of 0.5" with k value = 0.84", R value = 6 or greater.
Thermal floor protection is not required if the unit is raised 3.5" minimum (measured
from the bottom of the stove). However, standard ember floor protection is required.
It will need to be a non-combustible material that covers 16" (406 mm) in the US and
18" (450 mm) in Canada to the front of the unit and 8" (200 mm) to the sides.
If the unit is not raised, thermal floor protection required is 18" (450 mm) in the
US and Canada.
All floor protection must be non-combustible (i.e., metals, brick, stone, mineral
fi ber boards, etc.) Any organic materials (i.e. plastics, wood paper products, etc.)
are combustible and must not be used. The floor protection specified includes
some form of thermal designation such as R-value (thermal resistance) or k-factor
(thermal conductivity).
The fire prevention guy for the town said I pretty much just need spark protection, even a hearth rug. I think not......
So, a mason is going to install about an additional foot more of hearth (flush to the floor in front of the existing hearth). By removing carpet, adding some type of backer board and tile or stone as the top layer. The stone will be continued over the brick for continuity.
From what I read here, it seems ok but this R value stuff baffles me! I guess it might come down to the raised 3.5" requirement. Does the existing built in hearth = raised the depth of a brick plus the concrete or does it not count because that same hearth is floor level??
Does this meet the manual requirements to cover me in case of incident?
Thanks in advance!
Nervous Nellie!