Head calculations for HE?

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.
  • Hope everyone has a wonderful and warm Thanksgiving!
  • Super Cedar firestarters 30% discount Use code Hearth2024 Click here
Status
Not open for further replies.

MarkW

Member
Apr 5, 2013
201
NE Ohio
I have a 16x18 and 12x12 exchangers and wonder if anyone might suggest where I can find the head figures for these?
Thanks!
 
I have a 16x18 and 12x12 exchangers and wonder if anyone might suggest where I can find the head figures for these?
Thanks!
Are these for water to air? I've never seen anything those sizes in liquid to liquid.
the sizes of air HX's I use (from 18x18 to 24x24) all have a pressure drop of about 1'-2' head (1/2 to 1PSI) at the appropriate flow rates for the HX BTU output.
shot in the dark but hope it helps.
karl
 
Are these for water to air? I've never seen anything those sizes in liquid to liquid.
the sizes of air HX's I use (from 18x18 to 24x24) all have a pressure drop of about 1'-2' head (1/2 to 1PSI) at the appropriate flow rates for the HX BTU output.
shot in the dark but hope it helps.
karl


That data should be available from the manufacturer. The head, or pressure drop depends on the flow rate you intend to run through it.
 
Thanks Karl. That gives me something to go on.

Nothing available Bob. I suppose I could calculate the tube lengths and count all the elbows and come up with something that way but I'm just trying to get close.
I punched in some guess into a calculator app and came up with 9' for one of the HEs. I don't think that was quite right so I'll prefer to go with someone elses guess. ;)

Edit: Yes, it is liquid to air. Liquid to liquid would sure xfer the btu's at 16x18, huh!
 
Thanks Karl. That gives me something to go on.

Nothing available Bob. I suppose I could calculate the tube lengths and count all the elbows and come up with something that way but I'm just trying to get close.
I punched in some guess into a calculator app and came up with 9' for one of the HEs. I don't think that was quite right so I'll prefer to go with someone elses guess. ;)

Edit: Yes, it is liquid to air. Liquid to liquid would sure xfer the btu's at 16x18, huh!


fill it with water, dump it out and see how much fluid it holds. Measure the tube size, go online to CDA or one of the engineerstoolbox sites to see how many feet of tube that equates to. Count the u bends and calculate the 'footage' of tube that equals.

that's how we determine how long a buried pex loop is, measure the water contend and use the manufacturers data sheet for fluid capacity per foot, generally per 100 feet.
 
Clever idea.
 
I have spec sheet for a 20x20, and it lists .6 Ft head at 5 gpm, and 1.1 Ft head at 7 gpm. I can request other ones but that's the smallest I have on hand.
karl
 
Thanks Karl. That's more like it.
 