I need a simple, inexpensive solution to extend my hearth. I am only concerned about function at this point. The hearth is stone and flush with the floor. The floor is hard wood. I don't have a problem attaching something to the floor. When I re-finish the floor I will integrate something more permanent and aesthetically pleasing.
I have searched net stores and searched posts on hearth.com. It's still unclear to me how to go about finding something that meets the specs. The specs aren't even listed for most commercially available "hearth extenders."
For example:
http://www.walmart.com/ip/Minuteman...ender-in-Silver-Shine/15199683#Specifications
Here's what the manual says
Installation on a Combustible Floor
If the appliance is to be installed on a combustible floor or a combustible floor covering, it must
be installed on a 1†thick non-combustible millboard floor protector or a durable equivalent, with a
“R†factor of at least “1.5†(English units) or equivalent. The pad must be installed beneath the
unit, extending 16†(U.S.) on the side equipped with a door, and 8†on all other sides. The pad
must cover any horizontal chimney connector runs and extend 2†beyond each side.
Alternate Floor Protection:
An easy means of determining if a proposed alternate floor protector meets requirements is to
follow this procedure:
1) Convert specification to R-value:
i R-value is given – no conversion is needed
ii k-factor is given with a required thickness (T) in inches: R = 1/k x T
iii C-factor is given: R = 1/C
2) Determine the R-value of the proposed alternate floor protector:
i Use the correct formula given in step 1 (above) to convert values not expressed as “R.â€
ii For multiple layers, add R-values of each layer to determine overall R-value.
3) If the overall R-value of the system is greater than the R-value of the specified floor protector,
the alternate is acceptable.
I have searched net stores and searched posts on hearth.com. It's still unclear to me how to go about finding something that meets the specs. The specs aren't even listed for most commercially available "hearth extenders."
For example:
http://www.walmart.com/ip/Minuteman...ender-in-Silver-Shine/15199683#Specifications
Here's what the manual says
Installation on a Combustible Floor
If the appliance is to be installed on a combustible floor or a combustible floor covering, it must
be installed on a 1†thick non-combustible millboard floor protector or a durable equivalent, with a
“R†factor of at least “1.5†(English units) or equivalent. The pad must be installed beneath the
unit, extending 16†(U.S.) on the side equipped with a door, and 8†on all other sides. The pad
must cover any horizontal chimney connector runs and extend 2†beyond each side.
Alternate Floor Protection:
An easy means of determining if a proposed alternate floor protector meets requirements is to
follow this procedure:
1) Convert specification to R-value:
i R-value is given – no conversion is needed
ii k-factor is given with a required thickness (T) in inches: R = 1/k x T
iii C-factor is given: R = 1/C
2) Determine the R-value of the proposed alternate floor protector:
i Use the correct formula given in step 1 (above) to convert values not expressed as “R.â€
ii For multiple layers, add R-values of each layer to determine overall R-value.
3) If the overall R-value of the system is greater than the R-value of the specified floor protector,
the alternate is acceptable.