I’ve done extensive research on this specific job for well over a year and find this whole thing very confusing/ misleading. I acquired a beautiful hearthstone homestead stove and am in love with it.
I’ll be installing in an existing fireplace that had an old heat from heatilator and finally got around to removing that old beast.

I currently have a tile sub hearth with I’m assuming concrete underneath as in the basement it looks as the previous owner formed up and sistered the joists to support the concrete.

I have a small space 1000 sq ft so don’t want the thing to stick halfway out into my living room but seems that might be my only option as I can’t go much lower due to wooden Subfloor.

NOW, my problem is finding a clear directive on what is acceptable for a heart build for this stove.
Manual requires r value of 6.6 under the stove with 4” legs.

My question is, what has anyone who has this stove used to frame their hearths. The manual states non combustibles under the stove so does that mean I can’t use 2x4 to build a frame? Saw someone mention metal studs but doesn’t that conduct heat, I’m confused. Any explanations / help and specifically pictures (visual leaner) help!

My plan initially was
-self leveling concrete firebox and sub hearth
-durock
-2x4 frame
-fill the voids with mineral wool
-plywood? Or more durock, double layer?
-Finally mortar and tile or stone
I’ve yet to finalize what the finish product will be.

Is the idea there can be combustibles “in the hearth” as long as there is non combustibles (durock, mortar) underneath and on top the hearth? Also thought, has anyone used brick to make a frame? My thought with that is that wouldn't really be good for the load transfers of the stove.
The other thing with the taking up the whole room thing, it states only need r value of 2.5 16” in front of the stove so is it acceptable to have a lower kind of step in front of the stove, or maybe I was thinking make a rounded or hexagon type front. Idk I’m reaching the point of paralysis by analysis and want to do right but man, this is a lot.

Thank you to anyone who can contribute!!

As you can see from first photo here, I didn’t have clearance for a hearth therefore the lintel needed to be moved and figured why not rip the old beast out while I was in there…. Started with grinder and sawzall and ended up using a plasma cutter. Here are some pics of my journey so far 😂

[Hearth.com] Hearthstone homestead hearth[Hearth.com] Hearthstone homestead hearth[Hearth.com] Hearthstone homestead hearth[Hearth.com] Hearthstone homestead hearth[Hearth.com] Hearthstone homestead hearth[Hearth.com] Hearthstone homestead hearth
 
Last edited by a moderator:
The Homestead on short legs has one of the highest hearth insulation requirements in the business. It take quite a bit of insulation to meet the R=6.6. The stove is designed to be on a totally non-combustible hearth with the short legs.

Can you post some pictures of the underside of the hearth in the basement? Is there wood underneath or just concrete?
 
The Homestead on short legs has one of the highest hearth insulation requirements in the business. It take quite a bit of insulation to meet the R=6.6. The stove is designed to be on a totally non-combustible hearth with the short legs.

Can you post some pictures of the underside of the hearth in the basement? Is there wood underneath or just concrete?
I must say begreen, I’m kind of star struck. I’ve seen you on the forums for a long time. Given this is my first post and you’re the first to respond I feel honored 🫡.

I don’t have any photos of the basement currently I’ll take some when I get home today but yes it’s wood in the basement. Almost looks as if they built it and didn’t take it out. But then again, im no engineer I don’t know how the concrete would hold without the wooden support?

When you say totally non combustible hearth that means no wood for the framing then? I’m by no means questioning your hearth knowledge here but based on my research seems as if a lot of people kind of ignore that whole principle.
 
I must say begreen, I’m kind of star struck. I’ve seen you on the forums for a long time. Given this is my first post and you’re the first to respond I feel honored 🫡.

I don’t have any photos of the basement currently I’ll take some when I get home today but yes it’s wood in the basement. Almost looks as if they built it and didn’t take it out. But then again, im no engineer I don’t know how the concrete would hold without the wooden support?

When you say totally non combustible hearth that means no wood for the framing then? I’m by no means questioning your hearth knowledge here but based on my research seems as if a lot of people kind of ignore that whole principle.
Here’s some photos of the basement. As you can see it’s not a convenient location, as 2 of the return ducts for the forced hot air are right below it and upon further investigation it looks like pretty shabby.
 

Attachments

  • [Hearth.com] Hearthstone homestead hearth
    IMG_1540.webp
    81.2 KB · Views: 32
  • [Hearth.com] Hearthstone homestead hearth
    IMG_1541.webp
    200.5 KB · Views: 35
  • [Hearth.com] Hearthstone homestead hearth
    IMG_1544.webp
    182.6 KB · Views: 38
I wouldn't get too star-struck. I have been on a long time, but there are definitely many other folks here that are super helpful and knowledgeable.

The hearth is definitely not code. There should not be any wood under the hearth. It may be that they left the form boards.

To build up to R=6.6, check out this table for the insulation levels of materials. It will take a few inches of micore to get close.
 
Okay that’s part of my concern here, knowing it’s not up to code.

My next question is, at what point on my hearth build for the wood stove is it considered not a worry that the old hearth is supported by wood?

This is where I’m totally confused. So when I build the new hearth, after laying self leveling concrete, durock, etc on top of the existing concrete, tile hearth. Wouldn’t that protect / separate the wood supports in the basement from the fire hazard or heat transfer?
 
If you look at the hearth materials chart in the posted link you'll see that concrete is not great insulation. That's why wood is not allowed below it. It would take about 7" to build up to R= 6.6

Concrete1" has an R value of:0.095

I'm also a bit concerned about the haphazard brick protection that has been exposed with the old metal fireplace removed. Is the back wall getting rebuilt?

It would be good to get a code check on this from bholler. There may be other considerations I am missing.
 
I have noted that concrete is not a good insulator that’s why I plan to build a hearth pad on top of the existing concrete and tile. Again that’s where my confusion is…

So long as I have met the appropriate r value of 6.6 on my new hearth pad, it shouldn’t matter there is wooden sub floor or for that matter wooden supports in the basement?

Yes that old work will be covered as this weeks project is finishing brick work. Determining the height I need for my lintel, re installing that. Then it’s on to the hearth pad. I’m no mason but here’s a pic of it so far. What a pain keeping things level, in a not so level home.
[Hearth.com] Hearthstone homestead hearth
 
Okay that’s part of my concern here, knowing it’s not up to code.

My next question is, at what point on my hearth build for the wood stove is it considered not a worry that the old hearth is supported by wood?

This is where I’m totally confused. So when I build the new hearth, after laying self leveling concrete, durock, etc on top of the existing concrete, tile hearth. Wouldn’t that protect / separate the wood supports in the basement from the fire hazard or heat transfer?
Your hearth definitely does not meet requiments. Is your liner insulated the whole way down to the old smoke chamber area?
 
I have noted that concrete is not a good insulator that’s why I plan to build a hearth pad on top of the existing concrete and tile. Again that’s where my confusion is…

So long as I have met the appropriate r value of 6.6 on my new hearth pad, it shouldn’t matter there is wooden sub floor or for that matter wooden supports in the basement?

Yes that old work will be covered as this weeks project is finishing brick work. Determining the height I need for my lintel, re installing that. Then it’s on to the hearth pad. I’m no mason but here’s a pic of it so far. What a pain keeping things level, in a not so level home.View attachment 350263
Correct as long as you meet required r value you will be fine. But i am worried about how much masonry there is between the liner and combustibles above there
 
Correct as long as you meet required r value you will be fine. But i am worried about how much masonry there is between the liner and combustibles above there
It would help if the current hearth extension thickness was determined. Although it's improper with the wood form below, can he count on the concrete currently in the hearth extension as part of the insulation needed to reach R=6.6? If it's 8" thick it seems like it should be close or over the requirement.
 
Thank you for the clarification bholler.

As far as your masonry question I’m a little confused. Are you asking about how much masonry there is from the existing opening to the top of the mantle in front of the fireplace or are you asking about the inside where the liner is stick down?

As far as the liner sticking down it is that low because I had it lined last year just to see how the stove would work and all, so I’ll be cutting it back a foot or maybe more after I figure out how tall my new hearth pad will be.

You can see from one of the pictures I added initially the old flue liner is stuffed with mineral wool around the stainless liner from the old smoke shelf up to the top. Which in reality is a lie because they did a crap Job insulating the old flue, I just say that because I’ll be stuffing it full before I put the stove back In.
 
Begreen I plan on building a completely new hearth pad on top of that existing hearth. I think that’s where I was confusing you, possibly. It seems bholler cleared that up, that if I meet the 6.6 r value on my new hearth pad which will sit on top of the old tile and concrete I will be fine…… think I’ve got that right ?
 
As long as the new hearth pad's combined R value with the existing hearth underneath meets or exceeds the requirement, it's ok. The construction details posted are a little confusing because of the terms used, but it may be ok. Post a sketch or two of the proposed new pad including the existing hearth extension underneath it.

Note that packing the old smokeshelf and damper area with mineral wool does not mean that the liner's clearance requirements are met. The chimney needs to not be touching combustibles all the way up. 2" clearance is needed for an interior chimney and 1" for exterior. If that clearance is not met, the liner should be insulated for its full length.
 
Yeah my apologies for the confusing terminology. Essentially my new hearth will sit on top of the existing.
Base layer being self leveler
Then durock,
framed with steel studs,
topped with durock,
mortar,
stone or tile.

I’ve yet to determine if I should leave the voids between the framing empty or stuff with mineral wool. According to my stoves manual an 1/8th of “horizontal still air” provides r value of .92.
I’m not sure what horizontal still air means but I plan to have an air gap of 3”+ whatever the width of the steel stud is. If that doesn’t count as horizontal still air I guess I’ll stuff with mineral wool.

For the liner insulation I’m a little confused when you say 2” clearance. Currently the stainless liner sits inside of the old clay flue tiles, which are obviously inside the brick chimney. So in between the clay tiles there is insulation all the way from the top down around the stainless.

Sorry if this is confusing I’m trying my best to provide all necessary details, as I’ve stated I’ve been going nuts trying to figure this all out.
 
The 2" is for the clearance requirement for the brick sides of an interior chimney to any combustibles. If this is not the case for the existing chimney, then insulating the liner helps it achieve zero-clearance status.
I’ve yet to determine if I should leave the voids between the framing empty or stuff with mineral wool. According to my stoves manual an 1/8th of “horizontal still air” provides r value of .92.
Where are these "voids" A sketch would help a lot here.