Heatilator GCDC42L (42", LP gas, glass-sealed logset with outside air via flue)

Gas valve: SRV24034(Heatilator & Quadra-Fire Robert Shaw Valve)
Pilot: Heatilator and Heat-n-Glo Propane Gas Pilot Assembly 4021-733
Hi-Limit: Heatilator High Limit Switch (SRV24967)

Pilot lights, holds, log set fires with wall switch. FP runs then 'poofs out' (I only saw it once, that's the best description I can give). It has stayed on anywhere from two hours down to less than a hour.

Gas tech came out and of course it would not perform, worked perfectly of course.

Thoughts?

Limit Switch-Gas Valve wiring.jpg
 

DAKSY

Full Time RVer
Staff member
Dec 2, 2008
9,694
Wherever we're parked
Disconnect the wiring from the wall switch & touch the ends together. What happens?
If it stays on, you may have a faulty wall switch. If the issue occurs without the switch, let us know.
 

EEProf

New Member
Nov 3, 2021
7
Wilmington, NC
Disconnect the wiring from the wall switch & touch the ends together. What happens?
If it stays on, you may have a faulty wall switch. If the issue occurs without the switch, let us know.
Interesting. I replaced the wall switch a year ago, just a SPST Decora, so that's not it (well, nothing is never 'not it' until the real cause is found).

I think it has to do with heat somehow. Something gets warm and then opens, closes, whatever. I may just put a jumper across the switch terminals to turn it on tonight. We typically put it on at about 6 PM and run it until 10 or so.
 

EEProf

New Member
Nov 3, 2021
7
Wilmington, NC
I tested the high limit, it closes in at ~350ºF and then reopens at ~250ºF or so...as it should.

Tonite, the FP stayed on about 40 minutes. Seems to be getting shorter, which I suppose means that we may be approaching a hard fail, which is always easier to diagnose.

So now it is either the GV or the pilot assy. Any suggestions on troubleshooting?
 

DAKSY

Full Time RVer
Staff member
Dec 2, 2008
9,694
Wherever we're parked
The thermopile should be generating 525+/- 25mV when only the pilot is lit.
When the burner is lit, the milliVolts will drip to around 220+/- 20 & hold steady.
Place the probes of a multimeter set to mV on the TP & TH-TP terminals in order to take
the readings. Report back with what readings you get.
 
  • Like
Reactions: EEProf