Hello, I’ve been reading through other similar Heatilator posts and haven’t really seen anything similar to my problem. This is a remote controlled unit which hasn’t been functional for nearly a year and a half.
I click the button to start the unit, the pilot lights and the main burner lights, but weakly. Literally you can watch the holes fill in the burner one by one. When this unit was installed in 2016, I seem to remember a whoosh when the main burner lit. When I toggle the remote between high and low flames, nothing changes in the lazy flame. I do hear the relay click inside the main burner solenoid.
I have checked the readings for the inlet and manifold pressures. Inlet measures 6 in and the manifold measures 4.5 in, which is a bit high. I don’t see any way to change the pressure. The valve itself is a Dexen 750-500 unit.
Any thoughts or suggestions would be greatly appreciated. Seems like all the elements are there, just can’t get that whoosh.
I click the button to start the unit, the pilot lights and the main burner lights, but weakly. Literally you can watch the holes fill in the burner one by one. When this unit was installed in 2016, I seem to remember a whoosh when the main burner lit. When I toggle the remote between high and low flames, nothing changes in the lazy flame. I do hear the relay click inside the main burner solenoid.
I have checked the readings for the inlet and manifold pressures. Inlet measures 6 in and the manifold measures 4.5 in, which is a bit high. I don’t see any way to change the pressure. The valve itself is a Dexen 750-500 unit.
Any thoughts or suggestions would be greatly appreciated. Seems like all the elements are there, just can’t get that whoosh.