I've long known that the ductwork system of my HVAC is un-balanced. In summer, the MBR gets 5-10 degrees cooler than the rest of the house; that's fine, and the reverse in the winter is fine too, since I heat almost exclusively with wood - and the MBR is cooler, not warmer. (In other words, the system directs way too much air to the MBR, in both winter and summer. It the summer, that's, good, because we like sleeping in a chilly room. It'd be a bad thing in the winter, because the bedroom would be too hot. Except we don't run the HVAC in the winter, because we heat with wood. And since the woodstove is in the living area, the bedroom is still cooler than the living area, which is what we prefer). So it's not a problem now, but still it needs to be addressed.
Examining the ducts, I can see what appears to be a simple way of at least partially remediating the issue. Here are a couple of photos ...
The lefthand photo shows the main trunk, where the furnace and indoor heat-pump coil feed into it. It's probably 8x24" in size. All the ducts for the MBR attach to it (to the right of the photo frame). Then, in the righthand photo, you can see where the trunk doglegs to the side to clear a foundation pier, and gets much smaller. Note where a couple of runs of 6" flexduct takeoff right after it narrows. Seems to me it'd be simple to move those takeoffs to the larger part of the trunk. One of them would even become a much shorter run (it's probably close to 20ft long now).
So this might not solve the problem, but it sure seems like it would help. But should I not do it, is it possible it might make things worse ? I believe I understand the "two foot rule", that takeoffs should be separated by at least 2ft (unless they're on opposite sides of the trunk ?) and separated by 2ft from where the supply attaches to the trunk.
Another factor, I bought a cheap digital manometer, and measured about 0.25 inH2O between the furnace output and the evaporator coil, and aboiut 0.57 where the duct from the filter grill attaches to the return side of the furnace. That seems kinda backwards. I have one of those washable filters (20x25" for a 2-1/2 ton system).
I suppose I should get some HVAC pros in, but I know some of you here know a lot about HVAC, and the engineer in me can't resist trying to fix it myself.
Examining the ducts, I can see what appears to be a simple way of at least partially remediating the issue. Here are a couple of photos ...
The lefthand photo shows the main trunk, where the furnace and indoor heat-pump coil feed into it. It's probably 8x24" in size. All the ducts for the MBR attach to it (to the right of the photo frame). Then, in the righthand photo, you can see where the trunk doglegs to the side to clear a foundation pier, and gets much smaller. Note where a couple of runs of 6" flexduct takeoff right after it narrows. Seems to me it'd be simple to move those takeoffs to the larger part of the trunk. One of them would even become a much shorter run (it's probably close to 20ft long now).
So this might not solve the problem, but it sure seems like it would help. But should I not do it, is it possible it might make things worse ? I believe I understand the "two foot rule", that takeoffs should be separated by at least 2ft (unless they're on opposite sides of the trunk ?) and separated by 2ft from where the supply attaches to the trunk.
Another factor, I bought a cheap digital manometer, and measured about 0.25 inH2O between the furnace output and the evaporator coil, and aboiut 0.57 where the duct from the filter grill attaches to the return side of the furnace. That seems kinda backwards. I have one of those washable filters (20x25" for a 2-1/2 ton system).
I suppose I should get some HVAC pros in, but I know some of you here know a lot about HVAC, and the engineer in me can't resist trying to fix it myself.