Where to start.. I've built my boiler out of 1/4 m.s. and I'm just about to the setting out side point of the build. I designed it to hold about 180 gallons water. I think I'm getting lost when I'm reading about total head pressure. Being a sheetmetal worker by trade, hydronics is kind of French to me.
I've bought a 18x20 coil that's supposed to be good for 137,000 btus at 15gpm. I've ran 2-3/4"4supply and return lines to the house that's about 150' of pipe one way. I put foam insulation on all the line and ran them in 6" corrugated pipe about 30" or so down.
Would I be better off if I made it a closed loop system? I'm from central Indiana so our winters don't get to bad for the most part. I appreciate any insight on how I can calculate everything.
I've bought a 18x20 coil that's supposed to be good for 137,000 btus at 15gpm. I've ran 2-3/4"4supply and return lines to the house that's about 150' of pipe one way. I put foam insulation on all the line and ran them in 6" corrugated pipe about 30" or so down.
Would I be better off if I made it a closed loop system? I'm from central Indiana so our winters don't get to bad for the most part. I appreciate any insight on how I can calculate everything.
Attachments
Last edited:
T of 20F, btuh would be about 35,000. Two 3/4" lines in each direction would double that. Now discount that by lower gpm due to additional system pump head, btu losses to the ground, and other unknowns, all lead to total btuh capacity likely to be substantially less. Using a 26-99 is a nice try, but I doubt even that robust circulator can do what you will want or need.