Hello first time poster I am looking to install a Osburn 2400 insert. I plan on getting it WETT certified after installation. In the manual it states I need 20" hearth extension from face of fireplace for over 6 ft² opening. I have 6.4 ft² opening and only 18" hearth extension.
Can those 2 inches be added to floor protection calculation to pass WETT ?
Will the inspector catch that 2 inch difference? Are those industry standard measurements so no insert will work
? Lastly what options do I have if I need to extend the hearth front?
Thanks Bob
Can those 2 inches be added to floor protection calculation to pass WETT ?
Will the inspector catch that 2 inch difference? Are those industry standard measurements so no insert will work
? Lastly what options do I have if I need to extend the hearth front?
Thanks Bob