Jotul install clearance to non-combustable

Jordan Posted By Jordan, Apr 25, 2018 at 1:09 PM

  1. Jordan

    Jordan
    New Member 2.
    NULL
    

    Apr 25, 2018
    8
    0
    Loc:
    emmett, idaho
    Have a Jotul 606 and 380 but the manuals only show install clearances to combustibles. Anyone know the clearances to non combustibles?
     
  2. Enplater

    Enplater
    New Member 2.
    NULL
    

    Jun 6, 2017
    47
    2
    Loc:
    NH
    Like a concrete wall or brick? I don't there is a min distance but someone will have to back me up on that. Maybe putting a 700 degree chunk of steel an inch away from a freezing concrete wall isn't a good thing, just seems better to have a little room.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  3. bholler

    bholler
    Minister of Fire 2.
    NULL
    

    Jan 14, 2014
    12,439
    2,444
    Loc:
    central pa
    Yeah no required clearances to noncombustibles
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  4. Jordan

    Jordan
    New Member 2.
    NULL
    

    Apr 25, 2018
    8
    0
    Loc:
    emmett, idaho
  5. bholler

    bholler
    Minister of Fire 2.
    NULL
    

    Jan 14, 2014
    12,439
    2,444
    Loc:
    central pa
    So you are not talking about a non combustible wall? It is a combustible wall with noncombustibles on it?
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  6. Jordan

    Jordan
    New Member 2.
    NULL
    

    Apr 25, 2018
    8
    0
    Loc:
    emmett, idaho
    Its a non-combustable wall protection. I thought combustables were defined as furniture, plaster, etc.
     
  7. bholler

    bholler
    Minister of Fire 2.
    NULL
    

    Jan 14, 2014
    12,439
    2,444
    Loc:
    central pa
    But what is behind that wall protection
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  8. begreen

    begreen
    Mooderator 2.
    NULL
    
    Staff Member

    Nov 18, 2005
    71,261
    10,464
    Loc:
    South Puget Sound, WA
    Just covering a stud wall with a non-combustible product does not make the wall non-combustible. The granite will conduct heat to the drywall and studs behind it. If there is a pure concrete wall behind the granite, then that is truly non-combustible. Otherwise. the closest you can bring the stove to a combustible wall is 12" and then only with a proper NFPA 211 wall shield.

    https://www.hearth.com/talk/threads/wood-stove-wall-clearances-primer.147785/#post-1987380
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  9. Jordan

    Jordan
    New Member 2.
    NULL
    

    Apr 25, 2018
    8
    0
    Loc:
    emmett, idaho
    Thanks for posting that link. Based on that Chart and the clearances to combustable with my stove(32") and the granite spaced from the wall at 1" allows for a 66% reduction. Thats about 11-12."
     
  10. bholler

    bholler
    Minister of Fire 2.
    NULL
    

    Jan 14, 2014
    12,439
    2,444
    Loc:
    central pa
    It is 12" that is the minum allowed unless specified by the manufacturer. And that is only if that granite is spaced off the wall 1" with noncombustible spacers and has atleast a 1" gap top and bottom to allow for airflow. And that 12" is to the combustibles not the granite.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  11. Jordan

    Jordan
    New Member 2.
    NULL
    

    Apr 25, 2018
    8
    0
    Loc:
    emmett, idaho
    That makes sense. Accept for the Air Gap at the bottom. How can you have an air gap at the bottom of the panel? from what I've seen the wall panels sit flat to the floor protection.
     
  12. bholler

    bholler
    Minister of Fire 2.
    NULL
    

    Jan 14, 2014
    12,439
    2,444
    Loc:
    central pa
    If you saw that it was wrong and provided no clearance reduction. You need air to be able to come in the bottom and flow freely up behind the panel and out the top.
     