You don't have the room for a wrap insulation, you'd need to use a pour down type like Thermix http://www.amazon.com/Chimney-Plus-Protech-Thermix-Insulation/dp/B002TNWEQY/ref=sr_1_2?ie=UTF8&qid=1411439362&sr=8-2&keywords=chimney insulation
I'm not certain on the rigid, but I can say that I had a tough time getting a 6 inch liner down a 7 1/4 square chimney where the tiles were pretty darn straight. 5.5 inch might be the way to go.
How tall is your chimney? Exterior or interior chimney? How's its current condition? Are you sure if it has appropriate gap from combustibles?
pen
Yes, almost always its best to insulate. The issue will be getting an insulated 6" liner down the clay flue without breaking it out.
Take a standard paint can, 6 1/2" diameter, and lower it with a rope to see if you can get it down the chimney. If you can you have a reasonable shot of insulating it. But remember that the inside of the pipe is six inches, not the outside. For windage sake, figure the pipe to be six and a quarter. Add a 1/2" insulation blanket and you are pretty much out of space to get it down there. But mortar joints and misaligned flue tiles will ruin your whole day.
Hi Frank, I believe that the poured in insulation is dry, it's dumped in to fill the empty space.
My understanding is that you may need an insulated liner if your chimney doesn't have the required clearances.
If its a modern home, then you may have them. I would recommend you have it inspected by someone who can verify it.
On my installation, it's an external chimney. I can look up inside and see the one inch gap between the chimney and the combustible wall sheathing (the inside wall, of the room where I am located). If yours is an inside wall the the requirement is two inches. There's also other clearance requirements. Take a look at the following link to get an idea of the external chimney like mine, you'll be able to find one for in internal chimney with a little searching: http://www.rumford.com/code/clearances.html
Good luck!
Bruce.
pour in is not dry it is a dry mix that you mix with water. But to have proper insulation you need 1" or insulation which you will not get. Thia is why we break out liners in situations like this. That being said some insulation is better than none.
I would personally go with a 5.5 inch liner. You can use one with a 30-NC, and it will make installing the liner and insulation easier.
Check out double wall insulated rigid. But it is only going to fit if the existing liner is straight with no major cement gobs at the joints, which is more common than not.
On my installation, it's an external chimney. I can look up inside and see the one inch gap between the chimney and the combustible wall sheathing (the inside wall, of the room where I am located). If yours is an inside wall the the requirement is two inches
Bruce - I don't understand how you can "see" the 1" clearance requirement by "looking up inside". The clearance is measured from the exterior of the masonry (the side that faces the house) to the EXTERIOR shiething of the house. How can you see this from the inside wall, and how could you see it from the outside without ripping off siding?
That would remove a lot of headaches if I have to insulate. How do you know that stove can use that size. The manual only talks about 6 inch.
You can search here for threads where people have done it, and I was in a similar situation with a small, clay lined flue, so my 30 is connected to a 5.5 inch flex liner, wrapped with 1/2 inch insulation. My chimney is on the short side, but other than that, it works just fine as long as it's pretty cold out.
I have the clearances described in 1001.15 for an interior chimney. I have a clay lined 7x7 chimney in good condition. This said, is there any merit in running a 6" uninsulated steel flex? I'm now thinking if not insulated and the chimney and tile is in good shape, what is the advantage of running steel flex?