The readings are confusing. The catalyst and flue temperatures are the reverse of where I would expect them to be at. The flue is too hot and the cat is on the low side. Were the readings taken with the bypass open?
These temps are when the damper is open and I'm building up to the temperature I need to be at to engage the cat. The cat thermometer and the stove top thermometer are pretty close, so I'm not worried about them. I can get them up in the 800-900 range easy. The condar —18" above the stove on double pipe is out of wack! Wondering if it is a bad one...bought directly from condar.
These temps are when the damper is open and I'm building up to the temperature I need to be at to engage the cat. The cat thermometer and the stove top thermometer are pretty close, so I'm not worried about them. I can get them up in the 800-900 range easy. The condar —18" above the stove on double pipe is out of wack! Wondering if it is a bad one...bought directly from condar.
That explains it. The stove pipe temp looks right if the bypass is open. Most of the heat is going directly up the flue. Engaging the bypass should cause the flue temp to go down and the cat temp to come up.